A mechanical room is 40 ft by 30 ft by 12 ft high. If temporary exhaust is set for 6 air changes per hour, what exhaust rate is required?

Correct Answer

D) 1,440 cfm

Room volume is 40 x 30 x 12 = 14,400 cf. Six air changes per hour require 14,400 x 6 / 60 = 1,440 cfm. Other choices use the wrong room height, omit the hour-to-minute conversion, or use 10 ACH.

Answer Options
A
1,200 cfm
B
1,800 cfm
C
2,400 cfm
D
1,440 cfm

Why This Is the Correct Answer

Room volume is 40 x 30 x 12 = 14,400 cf. Six air changes per hour require 14,400 x 6 / 60 = 1,440 cfm. Other choices use the wrong room height, omit the hour-to-minute conversion, or use 10 ACH.

Was this explanation helpful?

More NASCLA Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your Florida General Contractor exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.