A mechanical room is 40 ft by 30 ft by 12 ft high. If temporary exhaust is set for 6 air changes per hour, what exhaust rate is required?

Correct Answer

D) 1,440 cfm

Volume = 40 × 30 × 12 = 14,400 cubic feet. Six changes per hour require 86,400 cubic feet per hour, or 1,440 cfm. The other rates correspond to 5, 7.5 and 10 ACH. The supplied 6 ACH is an exercise target, not proof that an actual hazardous atmosphere is safe.

Answer Options
A
1,200 cfm
B
1,800 cfm
C
2,400 cfm
D
1,440 cfm

Why This Is the Correct Answer

Volume = 40 × 30 × 12 = 14,400 cubic feet. Six changes per hour require 86,400 cubic feet per hour, or 1,440 cfm. The other rates correspond to 5, 7.5 and 10 ACH. The supplied 6 ACH is an exercise target, not proof that an actual hazardous atmosphere is safe.

Independent practice; verify any reference hint against the edition and category permitted for your booking. Official exam and reference-list sources →

Was this explanation helpful?

More NASCLA Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.