Vertical reinforcing is required at 32 in. on center along an 80 ft CMU wall, with a bar at each end. Each bar length including splice projection is 15 ft. What total reinforcing length is needed?
Correct Answer
B) 465 lf
The wall length is 80 x 12 = 960 in. Spaces at 32 in. give 960/32 = 30 spaces, so 31 bars are needed with bars at both ends. Total length is 31 x 15 = 465 lf. Other choices: 450 lf counts only 30 bars, 480 lf rounds the bar count upward incorrectly, and 405 lf uses a shorter bar length.
Why This Is the Correct Answer
The wall length is 80 x 12 = 960 in. Spaces at 32 in. give 960/32 = 30 spaces, so 31 bars are needed with bars at both ends. Total length is 31 x 15 = 465 lf.
Why the Other Options Are Wrong
Option A: 450 lf
vertical reinforcement, choice b: 450 lf backs into 15 when divided by 960/32; the accepted setup gives 15.5 on that same base.
Option C: 480 lf
vertical reinforcement, choice c: 32 x 15 gives 480 lf. That calculation follows multiplies those two listed numbers.
Option D: 405 lf
vertical reinforcement, choice d: 405 lf backs into 13.06 when divided by 31; the accepted setup gives 15 on that same base.
Memory Technique
Picture a checkpoint labeled vertical reinforcement: finish every operation before accepting 465 lf.
Reference Hint
Open Principles and Practices of Commercial Construction, 11th Ed., 2024; use the index entry or section for "Masonry reinforcing quantity takeoff" to confirm that The wall length is 80 x 12 = 960 in.
More NASCLA Questions
Bid instructions require bid security with each sealed bid. Which purpose should the estimator associate with that requirement?
A wood deck surface has 320 sf of coverage. Boards have a 5-1/2 in. actual face width, and the order includes an 8 percent cutting allowance. What linear footage is closest?
Using the dimensions shown for the stabilized construction entrance, what is the plan area?
A reroof area requires 14,720 sf of rigid insulation. Boards are 4 ft by 8 ft, and the order includes 5 percent waste. How many boards are needed?
Two addenda revise the drawings before bid day. What must a responsive bidder normally do with those addenda?
A utility trench is 180 ft long, 3 ft wide, and 7 ft deep with vertical sides inside a trench shield. What excavation volume is required?
A 120 ft long Type C trench is cut with a 4 ft bottom width and a 6 ft depth. If side slopes are 1-1/2 horizontal to 1 vertical, what excavation volume is closest?
A storm pipe run needs 240 ft of bedding, 4 ft wide and 6 in. thick. Including a 10 percent ordering allowance, how many cubic yards of bedding aggregate are needed?
A mass excavation produces 1,180 loose cubic yards of material for off-site disposal. End-dump trucks can haul 18 loose cubic yards per trip. What truck count is required?
An asphalt-shingle roof has a slope of 3:12. Under the IBC low-slope asphalt-shingle provisions, what underlayment arrangement is required?
People Also Study
Business & Financial Management
120 questions Β· 70% to pass
Contract Administration
60 questions Β· 70% to pass
Project Management
60 questions Β· 70% to pass