Under OSHA construction fire-protection rules, what is the maximum travel distance generally allowed to a 2A-rated fire extinguisher provided for ordinary combustible materials?
Correct Answer
A) 100 ft
OSHA construction rules require a 2A extinguisher for each 3,000 square feet or fraction, with travel distance not over 100 ft.
Why This Is the Correct Answer
OSHA construction rules require a 2A extinguisher for each 3,000 square feet or fraction, with travel distance not over 100 ft.
Why the Other Options Are Wrong
Option B: 25 ft
In general project requirements, 25 ft is the wrong selection for Fire extinguisher travel distance: 25 ft is a different published number than the cited Fire extinguisher travel distance value; OSHA 1926.150(c)(1)(i) supports 100 ft.
Option C: 300 ft
The trap in C is 300 ft. That selection is wrong because 300 ft is a different published number than the cited Fire extinguisher travel distance value; OSHA 1926.150(c)(1)(i) supports 100 ft; A 2A construction fire extinguisher is generally within 100 ft of travel.
Option D: Only the length of the building
Choice D gives Only the length of the building. Its specific error: it leaves the work at an informal or incomplete stage, while Fire extinguisher travel distance requires 100 ft. The accepted answer is 100 ft.
Memory Technique
Treat fire extinguisher travel distance like a labeled shelf; only the matching condition belongs with 100 ft.
Reference Hint
Open 29 CFR Part 1926 (OSHA Construction Standards), 1926-2023 / PSI OSHA Excerpts 2025; use 29 CFR 1926 Subpart F - Β§1926.150(c)(1)(i); hot-work fire prevention topics to confirm that OSHA construction rules require a 2A extinguisher for each 3,000 square feet or fraction, with travel distance not over 100 ft.
More NASCLA Questions
Bid instructions require bid security with each sealed bid. Which purpose should the estimator associate with that requirement?
A wood deck surface has 320 sf of coverage. Boards have a 5-1/2 in. actual face width, and the order includes an 8 percent cutting allowance. What linear footage is closest?
Using the dimensions shown for the stabilized construction entrance, what is the plan area?
A reroof area requires 14,720 sf of rigid insulation. Boards are 4 ft by 8 ft, and the order includes 5 percent waste. How many boards are needed?
Two addenda revise the drawings before bid day. What must a responsive bidder normally do with those addenda?
A utility trench is 180 ft long, 3 ft wide, and 7 ft deep with vertical sides inside a trench shield. What excavation volume is required?
A 120 ft long Type C trench is cut with a 4 ft bottom width and a 6 ft depth. If side slopes are 1-1/2 horizontal to 1 vertical, what excavation volume is closest?
A storm pipe run needs 240 ft of bedding, 4 ft wide and 6 in. thick. Including a 10 percent ordering allowance, how many cubic yards of bedding aggregate are needed?
A mass excavation produces 1,180 loose cubic yards of material for off-site disposal. End-dump trucks can haul 18 loose cubic yards per trip. What truck count is required?
An asphalt-shingle roof has a slope of 3:12. Under the IBC low-slope asphalt-shingle provisions, what underlayment arrangement is required?
People Also Study
Business & Financial Management
120 questions Β· 70% to pass
Contract Administration
60 questions Β· 70% to pass
Project Management
60 questions Β· 70% to pass