A floor under construction has 7,800 sf of protected building area. Using one 2A extinguisher per 3,000 sf or major fraction, how many extinguishers are required before travel-distance checks?

Correct Answer

C) 3 extinguishers

7,800 / 3,000 = 2.6, so the major fraction requires rounding up to 3 extinguishers before checking travel distance. Other choices round down, leave a fractional count, or add an unsupported extra unit.

Answer Options
A
2 extinguishers
B
2.5 extinguishers
C
3 extinguishers
D
4 extinguishers

Why This Is the Correct Answer

7,800 / 3,000 = 2.6, so the major fraction requires rounding up to 3 extinguishers before checking travel distance. Other choices round down, leave a fractional count, or add an unsupported extra unit.

Why the Other Options Are Wrong

Option A: 2 extinguishers

fire extinguisher count, choice a: 2 extinguishers counts a different spacing, panel, or repeated member quantity.

Option B: 2.5 extinguishers

fire extinguisher count, choice b: 2.5 extinguishers is wrong because 2.5 extinguishers counts a different spacing, panel, or repeated member quantity.

Option D: 4 extinguishers

fire extinguisher count, choice d: 4 extinguishers counts a different spacing, panel, or repeated member quantity.

Memory Technique

Say the fire extinguisher count rule aloud as a chain; the chain ends at 3 extinguishers, not an intermediate stop.

Reference Hint

Open 29 CFR 1926 OSHA Construction Standards; use 29 CFR 1926.150(c)(1)(i) to confirm that 7,800 / 3,000 = 2.6, so the major fraction requires rounding up to 3 extinguishers before checking travel distance.

Was this explanation helpful?

More NASCLA Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.