Wiring Methods & MaterialsTexas Journeyman Practice Questions

20 questions · 18% of the NEC Knowledge exam

Worked questions

1. What location classification applies to the interior of a raceway installed underground?

  • AIt is damp only when water is visible
  • BIt becomes dry when metal raceway is used
  • It is wet; use wet-location conductors
  • DIt is dry if the joints are glued

Why C is correct

Moisture can enter or condense in underground raceways even when joints are well made. The wiring method must therefore use conductor insulation identified for wet locations; raceway material does not change that classification.

2. For an angle pull containing large conductors, what primarily determines the required distance to the opposite wall?

  • AThe conductor insulation brand for the wiring method and location described
  • BThe box-cover paint color
  • Raceway trade sizes and their arrangement
  • DThe number of circuit breakers

Why C is correct

Angle- and U-pull dimensions are calculated from the raceway entries and arrangement so conductors can be pulled and bent without damage. Breaker count and appearance do not determine pull-box geometry.

16 more in the bank

Answers and explanations for these are in the app.

  • A cable emerges from a raceway sleeve with a sharp edge bearing on its jacket. What is required?
  • A cable passes through a framing hole too close to the nailing surface. What correction is appropriate?
  • A junction box containing conductor splices will be buried behind permanent finish. What must change?
  • A raceway is tied to ceiling-support wires not identified for electrical support. What should the installer do?
  • A raceway penetrates a tested fire-resistance-rated assembly. How should the opening be treated?
  • A raceway run has excessive total bends between pull points. What is the proper correction?
  • A white-insulated conductor is proposed as an ungrounded conductor without an allowed reidentification method. What should be done?
  • Several current-carrying conductors share one raceway in a hot space. Which effects must be evaluated?
  • When determining outlet-box fill, which items can require volume allowances in addition to insulated conductors?
  • A cable jacket is deeply cut during pulling, exposing damaged insulation. What is the proper response?
  • At a new outlet box, how much free conductor is generally required for splicing or device connection?
  • Before selecting burial depth for a branch circuit, what conditions must be checked in Table 300.5?
  • Conductors are installed in an outdoor raceway that appears watertight. How is the raceway interior classified?
  • May Type NM cable be installed in a raceway outdoors where the raceway interior is a wet location?
  • Type NM cable enters a single-gang nonmetallic box without an internal cable clamp. How close must it be secured to the box?
  • What information is needed to determine raceway fill for a conductor installation?