Motors & Generators — Texas Journeyman Practice Questions

4 questions · 8% of the Calculations exam

Worked questions

2. A single continuous-duty motor is covered by the 2026 NEC motor full-load-current tables. The applicable table value is 28 amperes, and no special motor rule or exception applies. What minimum branch-circuit conductor ampacity is required before any additional installation adjustment?

  • A22.4 amperes
  • B28 amperes
  • C56 amperes
  • 35 amperes

Where to look it up

https://www.elightinformation.com/post/motor-and-welding-machine-calculation-steps-2026-nec

Why D is correct

28 A × 125% = 35 A, D. This establishes the conductor-ampacity floor for the stated motor case. It does not select an AWG size or an overload setting; final conductor selection must also meet installation and terminal limits. Source: E Light Electric, Motor and Welding Machine Calculation Steps 2026 NEC, motor-circuit selection section: https://www.elightinformation.com/post/motor-and-welding-machine-calculation-steps-2026-nec