1. A new building has both a qualifying concrete-encased electrode and qualifying metal underground water pipe, with both electrode connections accessible before concealment. Under the general grounding-electrode-system rule in 2026 NEC 250.50, what is the required treatment?
- AUse only the concrete electrode and cut the water-pipe bond
- BUse only the water pipe and isolate the concrete electrode
- Bond both into the grounding electrode system
- DBond each electrode to a different downstream neutral
Where to look it up
https://www.nctcog.org/getContentAsset/662260f2-2502-4ea3-b6fb-794bdd432cc1/dfc3d011-8f63-43f6-9ed8-4b444333a1d0/RCCC-PPT_2026_04-28_External.pdf?language=en-US
Why C is correct
C, bond both into one grounding electrode system. Both qualifying electrodes are present; choosing only one does not satisfy the rule. Bonding each to a different downstream neutral is not an alternative to forming that electrode system. This question concerns accessible electrodes in new construction, not the treatment of inaccessible concrete reinforcement in an existing building. Source: NCTCOG, April 28, 2026 Regional Codes Coordinating Committee presentation, PDF page 27, unchanged first paragraph of 250.50: https://www.nctcog.org/getContentAsset/662260f2-2502-4ea3-b6fb-794bdd432cc1/dfc3d011-8f63-43f6-9ed8-4b444333a1d0/RCCC-PPT_2026_04-28_External.pdf?language=en-US . The separately underlined North Texas proposal about an electrode covered before inspection is not applied here.