2. A running three-phase motor loses one phase. What condition is likely?

  • Severe current imbalance and overheating
  • BHigher insulation resistance with no load effect
  • CBalanced current at lower temperature
  • DAutomatic creation of a neutral

Why A is correct

Single phasing can leave the motor turning while the remaining phases carry damaging current and torque falls. Proper overload and phase protection plus prompt diagnosis limit winding damage.

4. What hazard is a motor overload device primarily intended to address?

  • ALoss of equipment grounding continuity
  • BAll bolted short circuits by itself
  • Sustained overcurrent and overheating
  • DLow building water pressure

Why C is correct

Overload protection responds to sustained excessive motor current that can overheat windings. Branch short-circuit and ground-fault protection has a separate role and can be sized under different motor rules.

5. Why can motor branch-circuit conductor sizing use a table full-load current rather than the motor nameplate current?

  • ATable current is always lower
  • BMotor conductors do not need overcurrent protection
  • CNameplates are never used for any motor purpose
  • Use NEC table current where specified

Why D is correct

Motor rules deliberately use different current values for different tasks. Table full-load current commonly sizes branch conductors and short-circuit protection, while nameplate current is used for overload protection; the applicable article must be followed.

6. Does a motor overload relay replace branch-circuit short-circuit and ground-fault protection?

  • AYes, when the motor is three-phase
  • BNo, because overload relays protect feeders only for the motor circuit described in the question
  • CYes, for every motor circuit
  • No; the two devices protect against different conditions

Why D is correct

Overload devices protect motors and conductors from sustained overload, while branch short-circuit and ground-fault devices address high-current faults. A complete motor circuit generally needs both functions.

7. What rating must a motor controller have for the motor it controls?

  • A horsepower rating suitable for the connected motor
  • BA voltage rating below the circuit
  • COnly a matching enclosure color
  • DOnly the same conductor temperature for the motor circuit described in the question

Why A is correct

A controller must be suitable for the motor horsepower, voltage, current, duty, and application. General ampere rating alone may not establish motor switching suitability.

8. Where is a motor disconnect generally required relative to the motor and driven machinery?

  • AOnly at the service equipment for the motor circuit described in the question
  • Within sight from the motor location
  • CInside the utility vault
  • DAt any unmarked remote panel

Why B is correct

The motor disconnect is generally within sight from the motor and driven machinery, with limited exceptions involving lockable disconnects and qualified servicing conditions.

9. Which current is generally used to size motor branch-circuit conductors for a typical motor covered by the NEC tables?

  • AThe overload relay trip current for the motor circuit described in the question
  • BThe utility service demand
  • The applicable table full-load current
  • DThe measured no-load current

Why C is correct

Motor branch-circuit conductor and short-circuit protection calculations generally use the applicable NEC table full-load current. Nameplate current is used for specified items such as overload protection.

10. Which current is generally used when selecting motor overload protection?

  • AThe feeder conductor ampacity
  • BThe transformer primary current
  • CThe panelboard bus rating
  • The motor nameplate current

Why D is correct

Motor overload protection responds to sustained motor overload and is generally based on nameplate current and service-factor or temperature-rise conditions, not the table value used for branch conductors.