Which current is generally used to size motor branch-circuit conductors for a typical motor covered by the NEC tables?
- AThe overload relay trip current for the motor circuit described in the question
- BThe utility service demand
- The applicable table full-load current
- DThe measured no-load current
Why C is correct
Motor branch-circuit conductor and short-circuit protection calculations generally use the applicable NEC table full-load current. Nameplate current is used for specified items such as overload protection.