A motor has a 32-ampere nameplate current, and the problem supplies a permitted 115-percent overload setting. What setting results?
- A32 amperes
- B147.2 amperes
- 36.8 amperes
- D27.8 amperes
Why C is correct
Motor overload protection uses nameplate current for this calculation. Multiplying 32 amperes by the supplied 1.15 factor gives 36.8 amperes; this is distinct from branch-circuit conductor sizing.