A cast-in-place interior beam has stirrups and longitudinal reinforcement enclosed by forms, and the member will not contact soil or weather. Which cover is the ACI minimum for the beam reinforcement?

Correct Answer

A) 1-1/2 in. for beam reinforcement not exposed to weather

ACI 318-19 Table 20.6.1.3.1 lists 1-1/2 in. minimum cover for beams, columns, pedestals, and tension ties not exposed to weather or in contact with ground. Other choices: 3/4 in. is an interior slab, wall, or joist value; 2 in. applies to larger bars in formed exterior exposure, and 3 in. applies where reinforcement is cast against earth.

Answer Options
A
1-1/2 in. for beam reinforcement not exposed to weather
B
3/4 in. for interior slab, wall, or joist reinforcement
C
2 in. for larger bars in formed exterior concrete
D
3 in. for reinforcement cast against earth

Why This Is the Correct Answer

ACI 318-19 Table 20.6.1.3.1 lists 1-1/2 in. minimum cover for beams, columns, pedestals, and tension ties not exposed to weather or in contact with ground.

Why the Other Options Are Wrong

Option B: 3/4 in. for interior slab, wall, or joist reinforcement

In concrete work, 3/4 in. for interior slab, wall, or joist reinforcement is the wrong selection for Concrete cover - interior beam reinforcement: 3/4 in.

Option C: 2 in. for larger bars in formed exterior concrete

The trap in C is 2 in. for larger bars in formed exterior concrete. That selection is wrong because 2 in. for larger bars in formed exterior concrete is a concrete-cover value for a different exposure/member case; ACI 318-19 Table 20.6.1.3.1 keys this item to 1-1/2 in.

Option D: 3 in. for reinforcement cast against earth

Choice D gives 3 in. for reinforcement cast against earth. Its specific error: 3 in. for reinforcement cast against earth is a concrete-cover value for a different exposure/member case; ACI 318-19 Table 20.6.1.3.1 keys this item to 1-1/2 in.

Memory Technique

Make concrete cover - interior beam reinforcement a tabbed card: cite the exact condition, then choose 1-1/2 in. for beam reinforcement not exposed to weather.

Reference Hint

Open ACI 318-19, Building Code Requirements for Structural Concrete; use ACI 318-19 Table 20.6.1.3.1 to confirm that ACI 318-19 Table 20.6.1.3.1 lists 1-1/2 in.

Was this explanation helpful?

More NASCLA Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.