You are installing electrical service for a new 2,500 square foot home. The calculated electrical load is 28,000 watts. What is the minimum service size required in amperes at 240 volts?

Correct Answer

D) 117 amps

Current = Power ÷ Voltage = 28,000 watts ÷ 240 volts = 116.7 amps. This would require a minimum 150-amp service, but the calculated load is 117 amps.

Answer Options
A
150 amps
B
200 amps
C
100 amps
D
117 amps

Why This Is the Correct Answer

Using Ohm's Law: Current (Amps) = Power (Watts) ÷ Voltage (Volts) = 28,000 ÷ 240 = 116.67 amps. Rounded to a whole number, this is approximately 117 amps. The question asks for the calculated load in amps, not the next standard service size.

Why the Other Options Are Wrong

Option A: 150 amps

150 amps is a standard service size that would be selected if you were choosing the next available panel size above 117 amps. However, the question asks for the calculated load, not the standard panel size to install.

Option B: 200 amps

200 amps is a common residential service size but is larger than required by the calculated load. It would be an over-specification for this scenario.

Option C: 100 amps

100 amps is smaller than the calculated load of 116.67 amps and would be insufficient, potentially causing breaker trips or a fire hazard. Service must meet or exceed calculated load.

Memory Technique

P = IV, so I = P/V. 'PIV' — Power equals Current times Voltage. Rearrange: Current = Power ÷ Voltage. For this problem: 28,000 ÷ 240 ≈ 117 amps.

Was this explanation helpful?

More Michigan Questions

A residential foundation wall in Michigan is 8 feet high with 2 feet above grade. The backfill exerts lateral pressure of 30 psf per foot of depth. What is the maximum lateral pressure at the bottom of the foundation wall?

A builder discovers that the electrical service entrance was installed without proper permits. According to Michigan law, what is the most appropriate next step?

What is the maximum allowable span for a 2x8 floor joist (Grade 2 Douglas Fir) at 16" O.C. with 40 psf live load and 10 psf dead load according to Michigan Building Code span tables?

According to Michigan Building Code, what is the maximum height of a wood-framed bearing wall using 2x4 studs with standard construction?

A homeowner requests to convert a bedroom into a bathroom on the second floor. What is the primary Michigan code concern the builder must address?

According to Michigan plumbing regulations, what is the minimum pipe size required for a water service line serving a single-family residence?

A contractor is building a basement foundation wall that is 8 feet high and will retain 6 feet of soil. What is the minimum wall thickness required by the Michigan Building Code for poured concrete?

A homeowner wants to install a gas fireplace in their living room. The contractor notices the existing gas line is 1/2 inch black iron pipe. For a 40,000 BTU fireplace with a 25-foot run, is this pipe size adequate according to Michigan gas code?

During a framing inspection, the building official notes that the contractor used 2x4 studs at 24 inches on center for an exterior wall. According to Michigan Building Code, what is the maximum wall height allowed for this configuration?

A contractor is installing a beam to support floor joists. The beam must carry a total load of 8,000 pounds over a 12-foot span. If the allowable fiber stress for the lumber grade is 1,200 psi, what is the minimum required section modulus?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.