A client's home fails the required blower door test for energy compliance. The test shows 6.2 ACH50, but the Michigan Energy Code requires 3.0 ACH50. What is the most appropriate next step?

Correct Answer

B) Identify and seal air leakage paths to meet the requirement

When a home fails the blower door test, the most appropriate action is to identify air leakage sources and perform air sealing work to meet the required 3.0 ACH50 standard.

Answer Options
A
Install additional mechanical ventilation to compensate
B
Identify and seal air leakage paths to meet the requirement
C
Request a variance from the local building department
D
Document the test results and proceed with final inspection

Why This Is the Correct Answer

When a blower door test reveals excessive air infiltration (6.2 ACH50 vs. required 3.0 ACH50), the correct response is to locate and seal the air leakage paths. The blower door pressurizes the house so the contractor can identify exactly where air is escaping (outlets, penetrations, framing gaps, etc.) and then perform targeted air sealing to bring the reading below the code threshold. This directly addresses the root cause of the failure.

Why the Other Options Are Wrong

Option A: Install additional mechanical ventilation to compensate

Installing additional mechanical ventilation does not reduce air infiltration — it compensates for poor air quality caused by leakage, but it does not fix the building envelope failure. Adding ventilation would actually increase energy use while leaving the compliance issue unresolved. The Michigan Energy Code requires the building to meet the air tightness standard, not work around it.

Option C: Request a variance from the local building department

Requesting a variance is not appropriate here because the code establishes a specific, measurable performance requirement (3.0 ACH50). Variances are for cases where compliance is physically impossible or creates extraordinary hardship — an air sealing failure does not meet that standard. The contractor must fix the work, not request permission to leave it deficient.

Option D: Document the test results and proceed with final inspection

Documenting the failure and proceeding with final inspection is not acceptable. The test failed; the home does not comply with the Michigan Energy Code. Proceeding to final inspection with a known code violation would result in a failed inspection and expose the contractor to liability.

Memory Technique

Remember: blower door test FINDS the holes, then you FILL the holes. Fail the test → Find leaks → Seal them → Retest. The solution to too much air leaking out is always to stop it from leaking — not to add a machine or ask for an exception.

Was this explanation helpful?

More Michigan Questions

A residential foundation wall in Michigan is 8 feet high with 2 feet above grade. The backfill exerts lateral pressure of 30 psf per foot of depth. What is the maximum lateral pressure at the bottom of the foundation wall?

A builder discovers that the electrical service entrance was installed without proper permits. According to Michigan law, what is the most appropriate next step?

What is the maximum allowable span for a 2x8 floor joist (Grade 2 Douglas Fir) at 16" O.C. with 40 psf live load and 10 psf dead load according to Michigan Building Code span tables?

According to Michigan Building Code, what is the maximum height of a wood-framed bearing wall using 2x4 studs with standard construction?

A homeowner requests to convert a bedroom into a bathroom on the second floor. What is the primary Michigan code concern the builder must address?

According to Michigan plumbing regulations, what is the minimum pipe size required for a water service line serving a single-family residence?

A contractor is building a basement foundation wall that is 8 feet high and will retain 6 feet of soil. What is the minimum wall thickness required by the Michigan Building Code for poured concrete?

A homeowner wants to install a gas fireplace in their living room. The contractor notices the existing gas line is 1/2 inch black iron pipe. For a 40,000 BTU fireplace with a 25-foot run, is this pipe size adequate according to Michigan gas code?

During a framing inspection, the building official notes that the contractor used 2x4 studs at 24 inches on center for an exterior wall. According to Michigan Building Code, what is the maximum wall height allowed for this configuration?

A contractor is installing a beam to support floor joists. The beam must carry a total load of 8,000 pounds over a 12-foot span. If the allowable fiber stress for the lumber grade is 1,200 psi, what is the minimum required section modulus?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.