Startup, Troubleshooting & MaintenanceCalifornia C-10 Practice Questions

36 questions · 16% of the C-10 Electrical Trade exam

Worked questions

1. A 24-volt control coil measures 0 volts while its controller is calling for operation. What should be verified next?

  • AReplace the branch-circuit breaker with a larger one
  • Trace the complete series control path
  • CBypass every safety switch
  • DIncrease the equipment grounding conductor size

Why B is correct

Zero volts at a commanded coil points to a loss in the control-power path or an open safety/control. Tracing the circuit safely identifies the open point; bypassing safeties or changing unrelated power components is improper.

3. What should be verified before first energizing a switchboard?

  • AOnly paint color
  • Pre-energization assembly, grounding, settings, and clearance checks
  • CTools left inside for adjustment
  • DOnly utility bill

Why B is correct

Pre-energization inspection catches mechanical, wiring, contamination, and setting errors without exposing personnel to avoidable energized work.

4. A newly installed personnel-protection device does not trip with its integral TEST control. What conclusion is justified?

  • AThe equipment grounding conductor should be removed for the described C-10 installation and documented operating conditions
  • BThe branch circuit is proven overloaded
  • The protective function was not demonstrated and the device or circuit needs evaluation
  • DReverse phase sequence is proven

Why C is correct

The best answer is: The protective function was not demonstrated and the device or circuit needs evaluation. Failure of the prescribed test means protection has not been verified; it does not by itself diagnose overload or phase sequence. The device and its supply/line-load connections should be evaluated. This transferred field condition tests the same installation or safety principle in a different project context. The other choices conflict with the cited rule, listing, safe-work process, or necessary diagnostic sequence.

5. Current is normal, but a newly coupled motor vibrates excessively. Which mechanical checks should be made?

  • AReverse neutral polarity for the described C-10 installation and documented operating conditions
  • BRemove overloads
  • CIncrease breaker rating
  • Alignment, mounting, bearings, balance, and load

Why D is correct

The best answer is: Alignment, mounting, bearings, balance, and load. Mechanical problems can damage a motor even when electrical current appears normal. Alignment and load checks should precede electrical protection changes. This transferred field condition tests the same installation or safety principle in a different project context. The other choices conflict with the cited rule, listing, safe-work process, or necessary diagnostic sequence.

31 more in the bank

Answers and explanations for these are in the app.

  • A battery energy-storage enclosure shows swelling cells and an unusual odor. What should the technician do first?
  • A battery system reports high temperature and abnormal odor. What is the first response?
  • A breaker trips only after a load runs for twenty minutes. What should be investigated?
  • A contactor coil receives rated voltage but chatters. What should be evaluated?
  • A GFCI device will not trip using its integral test function. What is the appropriate conclusion?
  • A motor has normal current but excessive vibration after coupling. What should be checked?
  • A PV array produces expected open-circuit voltage but nearly zero current under adequate irradiance when connected to the inverter. What is a reasonable next check?
  • A standby transfer switch transfers but fails to retransfer after normal power returns. What should be checked?
  • A three-phase motor has markedly unbalanced phase currents and is overheating. What should be checked before changing overload settings?
  • A three-phase pump runs backward after startup. What is the appropriate correction?
  • An insulation-resistance reading is unexpectedly low. What should be checked before condemning the feeder?
  • Before first energizing a new panel, what is the best sequence?
  • One PV string has normal open-circuit voltage but low operating current. What should be checked?
  • What should an electrical commissioning record contain?
  • Why should sensitive electronic equipment be isolated as directed before megohmmeter testing?
  • A breaker holds initially but opens after twenty minutes at steady load. Which conditions should troubleshooting examine?
  • A commissioned battery system reports high temperature and an abnormal odor. What action comes before routine diagnostic work?
  • A contactor has rated coil voltage yet chatters and will not seat consistently. What should be evaluated?
  • A controller calls for a relay, but zero volts are measured across its 24-volt coil. Which portion of the circuit should be traced next?
  • A feeder's insulation-resistance value is unexpectedly low after a rainy installation period. What should be ruled out before replacement is ordered?
  • A loaded three-phase motor overheats while its phase currents differ greatly. What should be investigated before raising overload settings?
  • A megohmmeter test is planned on wiring connected to electronic controls. Why must equipment be isolated according to instructions?
  • A new switchboard is mechanically complete and ready for first energization. Which sequence best controls the startup?
  • A newly energized circuit trips instantaneously twice. What should occur instead of another immediate reset?
  • A three-phase fan rotates backward on initial startup. What is the safe corrective method?
  • A transfer switch moves to standby but remains there after normal power is stable. Which control sequence elements should be tested?
  • An ESS cabinet has bulging cells, elevated temperature, and a chemical odor. What is the first defensible technician response?
  • Before a new switchboard is energized, which assembly, grounding, setting, and workspace checks belong in the record?
  • One PV string has normal open-circuit voltage but lower operating current than parallel strings. Which causes should be investigated?
  • The commissioning binder lists equipment but contains no measured results or open deficiencies. What information should be added?
  • Under full sun, a PV input has expected open-circuit voltage but almost no operating current. Which checks should come next?