A newly installed personnel-protection device does not trip with its integral TEST control. What conclusion is justified?

California C-10 exam practice question · Startup, Troubleshooting & Maintenance

A newly installed personnel-protection device does not trip with its integral TEST control. What conclusion is justified?

  • AThe equipment grounding conductor should be removed for the described C-10 installation and documented operating conditions
  • BThe branch circuit is proven overloaded
  • The protective function was not demonstrated and the device or circuit needs evaluation
  • DReverse phase sequence is proven

Why C is correct

The best answer is: The protective function was not demonstrated and the device or circuit needs evaluation. Failure of the prescribed test means protection has not been verified; it does not by itself diagnose overload or phase sequence. The device and its supply/line-load connections should be evaluated. This transferred field condition tests the same installation or safety principle in a different project context. The other choices conflict with the cited rule, listing, safe-work process, or necessary diagnostic sequence.