64 questions · 28% of the C-10 Electrical Trade exam

Worked questions

4. A cold-weather rooftop PV string is being designed. Which calculation establishes whether maximum DC voltage stays within equipment ratings?

  • The temperature-corrected series-circuit open-circuit voltage
  • BThe inverter enclosure color
  • CThe monthly utility bill
  • DThe AC panel directory length for the described C-10 installation and documented operating conditions

Why A is correct

The best answer is: The temperature-corrected series-circuit open-circuit voltage. PV maximum voltage is derived from source-circuit open-circuit voltage with the applicable temperature correction. Utility consumption and physical appearance do not determine the maximum DC voltage. This transferred field condition tests the same installation or safety principle in a different project context. The other choices conflict with the cited rule, listing, safe-work process, or necessary diagnostic sequence.

5. A service upgrade depends on utility-furnished transformation and metering. Which issues should be coordinated before committing the project schedule?

  • AOnly branch receptacles
  • BOnly interior lighting
  • COnly final paint
  • Utility rules, fault data, schedule, and scope

Why D is correct

The best answer is: Utility rules, fault data, schedule, and scope. Utility scope can control design approval, equipment, easements, outage, lead time, and energization. Late coordination can delay the entire electrical project. This transferred field condition tests the same installation or safety principle in a different project context. The other choices conflict with the cited rule, listing, safe-work process, or necessary diagnostic sequence.

6. An indoor battery system is added beside occupied space. Which listing, disconnecting, and fire-safety items belong in coordination?

  • AOnly wall color
  • BOnly battery voltage for the described C-10 installation and documented operating conditions
  • COnly utility rate
  • Required listing, disconnects, and fire controls

Why D is correct

The best answer is: Required listing, disconnects, and fire controls. Energy storage introduces stored fault energy, fire, chemical, access, shutdown, and environmental issues. The complete listed system and applicable building and fire requirements control. This transferred field condition tests the same installation or safety principle in a different project context. The other choices conflict with the cited rule, listing, safe-work process, or necessary diagnostic sequence.

7. Millwork shown on the latest drawing occupies the required space in front of a panel. What needs resolution before the price is finalized?

  • AInstall a larger main breaker
  • BMount the panel behind the shelving
  • Revise the layout to preserve required working space and access
  • DTreat movable shelf doors as working clearance for the described C-10 installation and documented operating conditions

Why C is correct

The best answer is: Revise the layout to preserve required working space and access. Electrical working space must remain clear for operation and maintenance. Shelving obstructs access, and changing the breaker rating has no relationship to the physical safety requirement. This transferred field condition tests the same installation or safety principle in a different project context. The other choices conflict with the cited rule, listing, safe-work process, or necessary diagnostic sequence.

57 more in the bank

Answers and explanations for these are in the app.

  • A 120-volt circuit is expected to drop 6 volts at design load. What percent voltage drop is that?
  • A 15-kVA single-phase transformer has a 240-volt secondary. What is the full-load secondary current?
  • A 240-volt single-phase generator is rated 18 kVA. Using I = VA ÷ V, what rated current corresponds to that output?
  • A 240-volt single-phase resistive load draws 18 amperes. What is its power?
  • A 32-amp load is expected to operate continuously. Ignoring any special listed assembly, what minimum branch-circuit ampacity is required?
  • A balanced 480-volt three-phase load draws 30 amperes at unity power factor. Approximately how much real power does it use?
  • A battery has 12 kWh of usable energy and supplies a steady 3 kW load. Ignoring conversion losses, how long can it support the load?
  • A battery system is planned inside an occupied building. What should the estimate coordinate?
  • A crew of two electricians is scheduled for three 8-hour days. How many labor-hours should the estimate carry?
  • A design relies on an energy-management system to avoid a service upgrade for EV charging. What should be verified?
  • A dry-type transformer is added in a small electrical room. What scope must be coordinated?
  • A job needs 240 feet of raceway. The estimator adds 8 percent for waste and field changes. How many feet should be carried before rounding to purchasable lengths?
  • A long branch circuit meets minimum ampacity but calculated voltage drop is excessive. What is the appropriate design response?
  • A new service requires utility transformer and meter work. What should be coordinated early?
  • A plan lists motor horsepower but not the information needed for final branch-circuit selection. What should be obtained?
  • A project needs 375 feet of cable and carries 6 percent waste. What quantity results before purchase-length rounding?
  • A proposed device box will contain four insulated conductors, equipment grounds, an internal clamp, and one device yoke. How should the estimator verify box size?
  • A PV inverter is added to an existing panel. What must be reviewed at the connection point?
  • A renovation adds commercial cooking equipment to an existing service. What must be established before pricing breaker additions?
  • A rooftop PV project is being estimated. Which value is essential when checking the maximum DC system voltage?
  • A room layout places permanent shelving in front of a panelboard. What should occur before final pricing?
  • A route has multiple bends and congested pull points. What belongs in the takeoff?
  • A single-phase PV inverter delivers 7.2 kW at 240 volts at the stated operating point. Using I = P ÷ V, what output current does that represent?
  • A standby generator serves motor and nonmotor loads. What must the estimate consider?
  • An existing panel has two spare spaces. Before adding a 48-amp EV charging load, what must the contractor determine first?
  • Before pricing additional conductors in an existing raceway, which information is necessary for a defensible fill calculation?
  • Plans specify mounting listed equipment in an orientation prohibited by its instructions. What should the contractor carry in the estimate?
  • The available fault current at a new switchboard is greater than the marked interrupting rating of its main breaker. What must change?
  • The electrical drawings and specifications assign firestopping around penetrations to different trades. What is the best bid response?
  • A 120-volt branch circuit is calculated to lose 4.8 volts at design load. What is the voltage-drop percentage?
  • A 2026 permit project omits required lighting controls and acceptance testing from the drawings. What should the electrical bid carry?
  • A 240-volt single-phase heater draws 22 amperes. How much power does it consume?
  • A conduit route accumulates difficult bends before reaching the next accessible enclosure. What should the takeoff add?
  • A generator will start a large motor while supplying selected lighting and controls. Which loads and operating sequence govern sizing?
  • A listed PV inverter will connect to an existing bus. What must be checked at the proposed interconnection point?
  • A pull box contains conductors, grounding conductors, an internal clamp, and a device yoke. How should its required volume be established?
  • A remote 120-volt pump circuit has acceptable ampacity but unacceptable voltage drop at startup. Which design change is appropriate?
  • A restaurant remodel adds ovens and refrigeration to an older service. What must estimating establish before treating spare breaker spaces as usable capacity?
  • A takeoff contains 325 feet of conduit and a 7% waste allowance. What quantity should be carried before purchase-length rounding?
  • A tenant improvement adds a 48-ampere continuous EVSE to an older distribution system. What must be confirmed before a breaker is selected?
  • A transformer is squeezed into a storage room with little airflow and obstructed access. Which coordinated scope must be included?
  • An electric boiler draws 28 amperes for more than three hours. What minimum branch-circuit ampacity is required under the general 125% rule?
  • An estimate requires 460 feet of cable plus a 5% installation allowance. What quantity results before reel-length rounding?
  • An estimator wants to add a circuit to a partly occupied conduit. Which complete set of data is needed to check fill?
  • An EV energy-management system is used to cap building demand. What qualification must be verified before relying on it in the load calculation?
  • Clamp readings on a unity-power-factor three-phase test bank are 35 amperes per line, and the measured line voltage is 208 volts. What approximate input should appear on the power record?
  • Commissioning measurements show 480 volts line-to-line and 25 amperes on each phase of a resistive three-phase bank. Estimate its input kilowatts using the three-phase vector factor.
  • Door release, smoke control, and air-handler shutdown depend on the fire alarm. What must the electrical scope coordinate?
  • During acceptance testing, an electrician must set the expected secondary-current benchmark for a 25-kVA single-phase unit delivering 240 volts. What value should be recorded?
  • Five electricians each work three 8-hour shifts. How many labor-hours should be budgeted?
  • Four electricians are scheduled for two 9-hour shifts. How many labor-hours belong in the estimate?
  • Only horsepower appears on a motor schedule. Which additional data is needed to complete branch-circuit and starting design?
  • The architectural and electrical documents disagree about who seals rated penetrations. What should the C-10 bidder do?
  • The only available mounting position conflicts with the listed switchboard instructions. What should the bid include?
  • The riser diagram and equipment schedule specify different feeder conductors. What is the proper estimating response?
  • The utility revises available fault-current data above the value used for procurement. What needs to be reevaluated?
  • Utility data shows 50 kA available at equipment whose main device is marked 35 kA. What must the design team correct before installation?