A balanced 208-volt three-phase load draws 40 amperes at unity power factor. Using 1.732, what real power is used?

California C-10 exam practice question · Planning & Estimating

A balanced 208-volt three-phase load draws 40 amperes at unity power factor. Using 1.732, what real power is used?

  • A24.9 kilowatts
  • B8.32 kilowatts
  • About 14.4 kW
  • D5.2 kilowatts

Why C is correct

Balanced three-phase power is 1.732 times line voltage times line current at unity power factor. The result is about 14,410 watts, or 14.4 kilowatts.