Branch Circuit Conductors β€” Texas Master Practice Questions

23 questions Β· 16% of the NEC Knowledge exam

Worked questions

3. A healthcare facility has a 480V, 3-phase, 100A motor for a life support system. What is the minimum conductor size required for this motor circuit?

  • A6 AWG
  • 8 AWG
  • C10 AWG
  • D12 AWG

Exam tip

Special equipment such as life support systems often have specific code requirements for conductor sizing to ensure safety and reliability.

Why B is correct

According to 2026 NEC Article 680.41(A), the minimum conductor size for a 480V, 3-phase motor circuit for a life support system is 8 AWG. Larger conductors are not required for this application.

5. A residential kitchen has a total of 10 receptacles on a 20-ampere branch circuit. What is the minimum conductor size required for this circuit, according to 2026 NFPA 70 NEC?

  • 10 AWG
  • B12 AWG
  • C14 AWG
  • D16 AWG

Exam tip

Always check the specific requirements for kitchen circuits, as they often have different conductor size requirements.

Why A is correct

According to 2026 NFPA 70 NEC Article 210.21(B)(1), the minimum conductor size for a 20-ampere branch circuit in a kitchen is 10 AWG. The other options are larger sizes typically used for different applications.

7. A substation has a 600V, 3-phase feeder with a total load of 1200A. What is the minimum conductor size required for this feeder?

  • A250 kcmil
  • B300 kcmil
  • 350 kcmil
  • D400 kcmil

Exam tip

When dealing with feeders, it is important to refer to specific tables in the NEC to determine the correct conductor size.

Why C is correct

According to 2026 NEC Article 310.15(B)(16), the minimum conductor size for a 600V, 3-phase feeder with a 1200A load is 350 kcmil. Larger conductors are not required for this application.

8. An outdoor lighting system requires a 15A branch circuit. What is the minimum conductor size required for this circuit, considering it is installed outdoors?

  • 12 AWG
  • B14 AWG
  • C16 AWG
  • D18 AWG

Exam tip

Outdoor installations often have specific conductor size requirements to protect against environmental factors such as moisture and temperature.

Why A is correct

According to 2026 NEC Article 310.15(B)(16), the minimum conductor size for a 15A branch circuit installed outdoors is 12 AWG. Larger conductors are not required for this application.

12 more in the bank

Answers and explanations for these are in the app.

  • A 120/240-volt, 3-phase, 4-wire system is used in a commercial office building. What is the minimum conductor rating required for a 100-ampere load, according to 2026 NFPA 70 NEC?
  • A 30A branch circuit in a commercial building is protected by a 30A fuse. What is the maximum allowable conductor size for this circuit?
  • A 30A branch circuit is used for lighting in a commercial office building. Which type of overcurrent protection is required for this circuit?
  • A high-rise apartment building has a 200A, 120/240V branch circuit. Which type of overcurrent protection is required to prevent conductor overheating?
  • A hotel has a 20A, 120V branch circuit for kitchen appliances. Which type of overcurrent protection is required for this circuit?
  • A raceway in an office building has a total cross-sectional area of 100 square inches. What is the maximum allowable fill percentage, according to 2026 NFPA 70 NEC?
  • A residential kitchen requires a dedicated branch circuit for countertop appliances. Which conductor size is required for a 20A circuit, according to the 2026 NEC?
  • A retail store has a 20A branch circuit with a total load of 18A. What type of overcurrent protection is required for this circuit?
  • A retail store has a 30-ampere branch circuit with a 30-ampere circuit breaker. What is the maximum number of 15-ampere receptacles that can be safely installed on this circuit, according to 2026 NFPA 70 NEC?
  • A school district is installing a new branch circuit for computer labs. Which type of conductor protection is required to prevent physical damage in the floor raceway?
  • An industrial facility has a 100A, 480V motor that operates continuously. What is the minimum conductor size required for this motor circuit?
  • In an industrial facility, all electrical equipment must be bonded to the grounding system. Which of the following is the correct method for bonding electrical equipment, according to 2026 NFPA 70 NEC?

Practice all 23 Branch Circuit Conductors questions

Plus timed mock exams and a wrong book that follows you between the web and the app.