Services & Derived Systems β€” Texas Master Practice Questions

17 questions Β· 27% of the Calculations exam

Worked questions

2. A commercial building has a single 120/208-volt, 3-phase, 4-wire service. What is the minimum grounding electrode conductor size required?

  • 1/0 AWG
  • B3/0 AWG
  • C4/0 AWG
  • D6/0 AWG

Exam tip

Be aware of the specific requirements for grounding electrode conductor sizes based on the type of service and voltage.

Why A is correct

According to 2026 NFPA 70 NEC, a 120/208-volt, 3-phase, 4-wire service requires a minimum grounding electrode conductor size of 1/0 AWG. Options B, C, and D are incorrect as they are larger sizes suitable for different voltage and current requirements.

3. A healthcare facility is using armored cable (AC) for its wiring. What is the minimum size of the raceway required for this cable?

  • A1/2 inch
  • 3/4 inch
  • C1 inch
  • D1 1/4 inch

Exam tip

Check the specific requirements for raceway sizes based on the type of cable being used.

Why B is correct

According to 2026 NFPA 70 NEC, armored cable requires a raceway with a minimum size of 3/4 inch for 14 AWG to 10 AWG conductors. Options A, C, and D are incorrect as they are either too small or too large for the specified cable size.

6. A public building has a service entrance conductor with a rating of 600 amperes. What is the minimum grounding electrode conductor size required?

  • 3/0 AWG
  • B4/0 AWG
  • C250 kcmil
  • D300 kcmil

Exam tip

Be aware of the grounding electrode conductor requirements based on the service entrance conductor rating.

Why A is correct

According to 2026 NFPA 70 NEC, a service entrance conductor with a rating of 600 amperes requires a grounding electrode conductor of at least 3/0 AWG. Option B is incorrect as it is too large. Options C and D are incorrect as they are sizes suitable for different conductor ratings.

9 more in the bank

Answers and explanations for these are in the app.

  • A 20-ampere, 120/240-volt branch circuit is being installed in a residential kitchen. What is the minimum copper wire size required for this circuit?
  • A 20-ampere, 120/240-volt branch circuit is required for a kitchen range. What is the minimum conductor size required for this circuit?
  • A 600-volt, 3-phase, 4-wire system is used in an industrial facility. What is the minimum overcurrent protection required for a 100-ampere load?
  • A healthcare facility requires the installation of new medical equipment. What is the minimum grounding requirement for this equipment?
  • A public building requires the installation of new lighting fixtures. What is the minimum voltage required for a lighting circuit?
  • A residential building has a total of 20 lighting fixtures, each requiring 100 watts. Determine the minimum branch-circuit rating required for these fixtures, assuming a 120/240-volt, single-phase, 3-wire system.
  • A retail store has a service disconnecting means rated at 200 amperes. What is the minimum size of the overcurrent protection device required?
  • An educational institution is installing a new fire alarm system. What is the maximum distance between the fire alarm control unit and a manual fire alarm box?
  • An industrial plant has a motor that draws a maximum of 100 amperes at 480 volts. What is the minimum fuse rating required for this motor?

Practice all 17 Services & Derived Systems questions

Plus timed mock exams and a wrong book that follows you between the web and the app.