A 600-volt, three-phase substation feeder has an established required ampacity of 1200 amperes. It uses four identical parallel sets of copper THWN-2 phase conductors, each set in a separate raceway with not more than three current-carrying conductors at 30°C ambient. The specified termination ampacity limit is 75°C; all parallel-installation conditions are satisfied, and no correction, adjustment or other condition requires a larger size. What is the minimum conductor size in each set under 2026 NEC Table 310.16?

Texas Master exam practice question · Branch Circuit Conductors

A 600-volt, three-phase substation feeder has an established required ampacity of 1200 amperes. It uses four identical parallel sets of copper THWN-2 phase conductors, each set in a separate raceway with not more than three current-carrying conductors at 30°C ambient. The specified termination ampacity limit is 75°C; all parallel-installation conditions are satisfied, and no correction, adjustment or other condition requires a larger size. What is the minimum conductor size in each set under 2026 NEC Table 310.16?

  • A250 kcmil
  • B300 kcmil
  • 350 kcmil
  • D400 kcmil

Where to look it up

https://www.mikeholt.com/instructor2/img/product/pdf/1769017155.pdf

Why C is correct

Each of the four equal sets must provide at least 1200 / 4 = 300 A. At 75°C, 300 kcmil copper provides 285 A per set, or 1140 A total, and fails. The next size, 350 kcmil, provides 310 A per set, or 1240 A total, and meets the requirement. This answer depends on four properly installed parallel sets; a single 350 kcmil conductor does not carry 1200 A. Source: Mike Holt Enterprises, Understanding the 2026 National Electrical Code, Volume 1, public sample pages 366–367 (310.10(G)) and 379 (Table 310.16). https://www.mikeholt.com/instructor2/img/product/pdf/1769017155.pdf

Practice 23 more Branch Circuit Conductors questions

Timed mock exams, a wrong book and flashcards — one subscription covers every contractor exam line.

Start studying free