Combustion Air — Texas ACR A Practice Questions

12 questions · 5% of the Texas ACR A exam

Worked questions

2. For a newly installed boiler subject to the Texas TDLR Boiler Safety program, which state reporting step does TDLR identify?

  • ANo installation report is required.
  • BSend only a maintenance invoice to the local fire marshal.
  • Submit a Boiler Installation Report to TDLR within 30 days of installation.
  • DWait until the next annual inspection to report the installation.

Where to look it up

https://www.tdlr.texas.gov/boilers/blrfaq.htm

Why C is correct

TDLR identifies a Boiler Installation Report due within 30 days of installation. The boiler must not be test-fired or operated until the required initial inspection passes or a temporary operating permit is approved. This does not replace applicable local permits or the separate requirements for repairs and alterations.

4. A building has CO alarms and fuel-burning appliances. Which statement about the alarms is correct?

  • AThey make combustion-air provisions unnecessary.
  • They provide warning but do not replace proper appliance installation, venting and maintenance.
  • CThey prevent appliances from producing CO.
  • DTheir presence proves every flue is unobstructed.

Where to look it up

https://www.cpsc.gov/Safety-Education/Safety-Education-Centers/Carbon-Monoxide-Information-Center

Why B is correct

CO alarms warn of a hazard; they do not correct its source. Follow appliance installation and maintenance requirements as well as alarm instructions.

6. A school has recurring complaints near a fuel-burning appliance. Which response addresses a potential combustion hazard?

  • AAssume the last routine inspection rules out a current problem.
  • Have a qualified professional investigate the appliance and venting, following emergency procedures if CO is suspected.
  • CDisable the CO alarm to avoid interruptions.
  • DIncrease the thermostat setting without inspecting the appliance.

Where to look it up

https://www.cpsc.gov/Safety-Education/Safety-Education-Centers/Carbon-Monoxide-Information-Center

Why B is correct

A previous inspection does not rule out a new fault. Potential CO exposure requires prompt safety action and qualified investigation, not an invented fixed Texas testing interval.

7. A boiler-room design specifies 5,000 cfm of combustion-air supply. Two operating fans deliver 1,800 and 2,200 cfm. Ignoring interaction losses for this exercise, what additional capacity is needed?

  • A0 cfm
  • 1,000 cfm
  • C2,000 cfm
  • D4,000 cfm

Where to look it up

Explicit exercise assumptions; not a universal code requirement.

Why B is correct

Available flow is 1,800 + 2,200 = 4,000 cfm; shortfall = 5,000 − 4,000 = 1,000 cfm. Actual fan interaction must be checked in commissioning; no universal airflow-per-Btu factor is claimed.

8. A commercial kitchen has 10,000 cfm of total building exhaust and no other source of replacement air. Applying the approximately equal makeup-air principle described in 2024 IMC Section 508.1, approximately how much total makeup air is needed?

  • A100 cfm
  • B1000 cfm
  • 10,000 cfm
  • D1500 cfm

Where to look it up

https://www.iccsafe.org/building-safety-journal/bsj-technical/exhaust-systems-and-makeup-air-achieving-balance-under-the-2024-international-mechanical-code/

Why C is correct

Under the stated assumptions, approximately 10,000 cfm of makeup air balances the 10,000 cfm exhausted. All replacement-air sources must be considered in an actual design, and makeup air must not impair hood capture. A fire suppression system does not turn this into a 1% replacement-air calculation.

9. When planning commercial-kitchen makeup air, which quantity should be coordinated with the exhaust system?

  • AOnly the gas input rating of one burner.
  • BOnly the number of kitchen employees.
  • The total exhaust airflow and the replacement-air sources serving it.
  • DOnly the room thermostat setpoint.

Where to look it up

https://www.iccsafe.org/building-safety-journal/bsj-technical/exhaust-systems-and-makeup-air-achieving-balance-under-the-2024-international-mechanical-code/

Why C is correct

ICC explains makeup air in relation to total exhaust and capture performance. Burner input alone cannot establish a universal replacement-air flow.

3 more in the bank

Answers and explanations for these are in the app.

  • A hospital in Texas has a negative pressure room for isolation purposes. According to the 2024 IFGC, what is the minimum exhaust air flow rate required for this room?
  • A public building in Texas has a boiler that uses coal as fuel. According to the Texas Administrative Code Chapter 75, what is the maximum allowable carbon monoxide concentration in the exhaust gas from this boiler?
  • A residential building in Texas is equipped with a natural gas furnace. According to the 2024 IMC, what is the minimum outdoor air supply required for this furnace?

Practice all 12 Combustion Air questions