Ventilation β€” Texas ACR A Practice Questions

12 questions Β· 5% of the Texas ACR A exam

Worked questions

3. Apply the openable-area ratio in 2024 IMC Section 402.2 to a 250-square-foot bedroom. There are no other qualifying ventilation openings. What minimum total area openable to the outdoors is required by this ratio?

  • A5 square feet
  • B7 square feet
  • 10 square feet
  • D12 square feet

Where to look it up

https://www.iccsafe.org/building-safety-journal/bsj-technical/code-corner-2024-international-mechanical-code-chapter-4-ventilation/

Why C is correct

The rule uses 4% of the floor area being ventilated: 250 Γ— 0.04 = 10 square feet of openable area. This is not a universal bedroom window size; only the openable portion counts. The calculation does not determine emergency escape, light or other requirements.

4. A residential balancing report shows three supply terminals at 40, 35 and 25 cfm and two exhaust terminals at 45 cfm each. What is the measured supply-minus-exhaust difference?

  • A10 cfm more exhaust than supply.
  • 10 cfm more supply than exhaust.
  • CNo difference.
  • D100 cfm more supply than exhaust.

Where to look it up

Explicit exercise assumptions; not a universal code requirement.

Why B is correct

Supply totals 100 cfm and exhaust totals 90 cfm, so the difference is +10 cfm. This arithmetic does not predict building pressure without considering other air paths.

5. A ventilation unit uses a disposable, nonwashable air filter. Inspection shows that it has reached the manufacturer's replacement criterion. Which maintenance action is appropriate?

  • Replace it with the specified compatible filter using the prescribed service procedure.
  • BKeep operating indefinitely and only change the calendar schedule.
  • CInstall any higher-MERV filter without checking compatibility.
  • DWash and reuse the nonwashable filter.

Where to look it up

https://www.cdc.gov/infection-control/hcp/environmental-control/air.html

Why A is correct

Replace the disposable filter as specified after following the equipment service and isolation instructions. Washing a nonwashable filter or choosing a more restrictive filter without checking system compatibility is not an equivalent remedy.

6. How should inspection and replacement of ventilation air filters be scheduled?

  • Use manufacturer instructions and operating conditions; inspect and replace when specified criteria are met.
  • BReplace every six months even when damaged sooner.
  • CInspect only once a year regardless of condition.
  • DWait two years whenever the fan still runs.

Where to look it up

https://www.cdc.gov/infection-control/hcp/environmental-control/air.html

Why A is correct

Inspection and replacement are different actions. Follow the system and filter instructions, monitor condition and applicable pressure criteria, and act when service is needed. A universal three-month rule cannot be inferred for every filter.

6 more in the bank

Answers and explanations for these are in the app.

  • A commercial kitchen in Texas requires a ventilation system. According to the 2024 IFGC, what is the minimum exhaust air flow rate required for a commercial kitchen range hood?
  • A commercial office building in Texas requires a ventilation system. According to the 2024 IFGC, what is the minimum outdoor air supply required per square foot for office spaces?
  • A Texas industrial facility has a ventilation system that includes a carbon monoxide (CO) detection system. According to the Texas Administrative Code Chapter 75, what is the maximum allowable CO concentration in the workplace?
  • A Texas industrial facility has a ventilation system that includes a heat recovery ventilator (HRV). According to Modern Refrigeration and Air Conditioning 22nd ed., what is the typical efficiency range of an HRV?
  • An industrial facility in Texas requires a ventilation system for a hazardous area. According to the 2024 UMC, how should the ventilation rate be determined for this area?
  • In Texas, what is the recommended frequency for testing the functionality of a smoke control system in a public building?

Practice all 12 Ventilation questions