1. When sizing the branch-circuit conductors and the branch-circuit short-circuit and ground-fault protective device for a single continuous-duty motor, which current value must be used?
- AThe running current measured with a clamp meter after the motor is loaded
Clamp-meter readings change every time the driven load changes, so they cannot form a repeatable basis for conductor or breaker sizing. Field measurements are a troubleshooting tool, not a Code sizing input.
- The full-load current listed in the NEC motor tables for that horsepower and voltage
- CThe locked-rotor current stamped on the motor nameplate
Locked-rotor current describes the inrush when the rotor is stalled. It matters when selecting certain disconnect types and instantaneous-trip settings, but it never sizes branch-circuit conductors.
- DThe nameplate full-load amperes marked by the motor manufacturer
Nameplate full-load amperes are the correct basis for the running overload device only. Substituting the nameplate value for the table value is the single most common motor-circuit sizing error.
Why B is correct
Article 430 directs you to the motor full-load current tables, not the nameplate, whenever you size conductors, switches, and branch-circuit short-circuit and ground-fault devices. Using one standardized table value keeps every motor of a given horsepower and voltage on the same conductor and breaker, no matter which manufacturer built it.
What this question is testing
This question checks whether you can keep the two motor current sources separate in your head: table current drives conductors and short-circuit protection, nameplate current drives overload. Nearly every motor calculation on the exam starts with picking the right one, so a mistake here cascades through the rest of the problem.
On the job
A 10 hp 460-volt motor may be nameplated anywhere from about 12 to 13.5 amperes depending on the maker, but the table value stays constant. If the crew sizes conductors off nameplate and the customer later swaps in a different brand of the same horsepower, the circuit no longer complies. Sizing from the table means the conductors and breaker are already correct for any replacement motor of the same rating, which is why service shops can change a motor without pulling new wire.
Memory technique
Table for the wire, nameplate for the heater.
Exam tip
Read the stem for the words conductors or branch-circuit protection and reach for the table; read overload and reach for the nameplate.
Where to look it up
Article 430 Part I general provisions, the section on how motor full-load current is determined, then the motor full-load current tables at the end of Article 430.