1. When sizing the branch-circuit conductors and the branch-circuit short-circuit and ground-fault protective device for a single continuous-duty motor, which current value must be used?

  • AThe running current measured with a clamp meter after the motor is loaded

    Clamp-meter readings change every time the driven load changes, so they cannot form a repeatable basis for conductor or breaker sizing. Field measurements are a troubleshooting tool, not a Code sizing input.

  • The full-load current listed in the NEC motor tables for that horsepower and voltage
  • CThe locked-rotor current stamped on the motor nameplate

    Locked-rotor current describes the inrush when the rotor is stalled. It matters when selecting certain disconnect types and instantaneous-trip settings, but it never sizes branch-circuit conductors.

  • DThe nameplate full-load amperes marked by the motor manufacturer

    Nameplate full-load amperes are the correct basis for the running overload device only. Substituting the nameplate value for the table value is the single most common motor-circuit sizing error.

Why B is correct

Article 430 directs you to the motor full-load current tables, not the nameplate, whenever you size conductors, switches, and branch-circuit short-circuit and ground-fault devices. Using one standardized table value keeps every motor of a given horsepower and voltage on the same conductor and breaker, no matter which manufacturer built it.

What this question is testing

This question checks whether you can keep the two motor current sources separate in your head: table current drives conductors and short-circuit protection, nameplate current drives overload. Nearly every motor calculation on the exam starts with picking the right one, so a mistake here cascades through the rest of the problem.

On the job

A 10 hp 460-volt motor may be nameplated anywhere from about 12 to 13.5 amperes depending on the maker, but the table value stays constant. If the crew sizes conductors off nameplate and the customer later swaps in a different brand of the same horsepower, the circuit no longer complies. Sizing from the table means the conductors and breaker are already correct for any replacement motor of the same rating, which is why service shops can change a motor without pulling new wire.

Memory technique

Table for the wire, nameplate for the heater.

Exam tip

Read the stem for the words conductors or branch-circuit protection and reach for the table; read overload and reach for the nameplate.

Where to look it up

Article 430 Part I general provisions, the section on how motor full-load current is determined, then the motor full-load current tables at the end of Article 430.

2. The secondary of a transformer supplies a 208Y/120-volt system that has no direct electrical connection to the conductors of the supply system. How must this derived system be bonded and grounded?

  • AThe neutral point should be left unbonded and connected back to the main service equipment, where the main bonding jumper already sets the ground reference for the premises

    One bonding jumper at the service cannot serve a system that has no electrical connection to the supply conductors. Fault current on the secondary must return to the secondary windings, so an unbonded neutral may never draw enough current to open the device.

  • BA bonding jumper should be installed at every downstream panelboard so that fault current has several parallel return paths and the impedance of any single path cannot delay the operation of the overcurrent device

    Multiple jumpers put the grounded conductor and the equipment grounding system in parallel, so ordinary neutral current returns on conduit and ground conductors. That is objectionable current, and it produces stray voltage rather than faster clearing.

  • A system bonding jumper connects the derived grounded conductor to the equipment grounding conductors at one point, and a grounding electrode conductor runs from that same system to a suitable electrode
  • DThe equipment grounding conductor brought from the primary side serves as the complete grounding means for the secondary, because it already ties the transformer enclosure back to the service electrode

    The primary equipment grounding conductor bonds the enclosure, which is necessary but not sufficient. It never establishes the neutral-to-ground reference the derived system needs, and it leaves secondary faults with no defined return to the secondary windings.

Why C is correct

A separately derived system needs its own neutral-to-ground connection so that a line-to-ground fault on the secondary has a low-impedance path back to the derived source. Article 250 requires that system bonding jumper at exactly one location, plus a grounding electrode conductor from that same location to a suitable electrode.

What this question is testing

This tests recognition of a separately derived system and the three pieces that make it work: a single system bonding jumper, a grounding electrode conductor, and the supply-side bonding jumper carrying fault current back to the source.

On the job

Buildings with a stray-voltage or noisy-ground complaint frequently turn out to have a transformer bonded in two places, typically once at the transformer and again in the downstream panel where an installer left the factory bonding screw in place. Pull the covers, find every neutral-to-ground connection, and leave exactly one. Also confirm the grounding electrode conductor is sized from the largest derived ungrounded conductor and lands on a qualifying electrode such as building steel or a metal water pipe near the transformer.

Memory technique

One system, one bonding jumper, one electrode connection.

Exam tip

If the question says no direct electrical connection between primary and secondary conductors, it is a separately derived system, which brings the whole Article 250 derived-system package.

Where to look it up

Article 250 Part II, the section on grounding separately derived alternating-current systems, and the sizing table for the grounding electrode conductor of a derived system.

3. Recessed luminaires that are not identified for contact with insulation are installed in a ceiling that will be insulated from above. How must the thermal insulation be handled around those luminaires?

  • It must be kept at least 3 inches away from the luminaire enclosure, wiring compartment, and driver or ballast
  • BIt may be packed tightly against the housing as long as the installed lamp wattage is cut to half the marked maximum

    Reducing lamp wattage is not a recognized substitute for the required clearance. The listing of the luminaire, not the lamp installed in it, decides whether insulation may touch the housing.

  • CIt must be kept at least 12 inches clear on every side of the luminaire, including above it

    The 12-inch figure belongs to clothes closet luminaire clearances, not to thermal insulation around recessed fixtures. Applying it would sterilize far more attic area than the Code requires.

  • DIt may touch the housing provided the ceiling cavity includes a continuous vapor barrier

    A vapor barrier addresses moisture migration and has no effect on heat buildup in the luminaire housing or on the temperature the driver or ballast sees.

Why A is correct

A non-IC recessed luminaire relies on convection through the ceiling cavity to shed heat from its housing and driver. Article 410 protects that airflow by keeping insulation 3 inches away and out of the space directly above the fixture, unless the luminaire carries an insulation-contact identification.

What this question is testing

This tests whether you know the insulation clearance for recessed luminaires and can distinguish the Type IC listing from the separate half-inch clearance from combustible material that applies to the same fixture.

On the job

This shows up as a callback in the first winter after an energy retrofit, when blown-in attic insulation buries older non-IC cans and the thermal protectors start cycling the lights on and off. The fix is either restoring the 3-inch clearance with a rigid dam around each fixture or replacing the luminaires with IC-rated units. On new work, specify IC-rated airtight fixtures from the start, since energy codes push toward deep insulation and someone eventually blows over everything in the attic.

Memory technique

No IC marking means the insulation stays 3 inches back and never sits on top.

Exam tip

Two different recessed-luminaire clearances exist: 3 inches to insulation and a half inch to combustible material. Read which one the stem is asking about.

Where to look it up

Article 410 Part XI, clearance and installation requirements for recessed luminaires, covering both combustible material and thermal insulation.

4. A permanently connected appliance is rated over 300 volt-amperes. Under what condition is the branch-circuit switch or circuit breaker permitted to serve as the required disconnecting means for that appliance?

  • AOnly when the appliance draws under 30 amperes and is supplied by a dedicated individual branch circuit

    Ampere rating and circuit dedication are not the qualifying conditions. A 300 volt-ampere threshold determines which rule applies, but nothing in it keys on 30 amperes or on the circuit being individual.

  • When the switch or breaker is within sight from the appliance, or is capable of being locked in the open position
  • COnly when a qualified service technician is present during any energized work on the appliance

    Personnel qualifications are governed by workplace safety practice, not by the Code section that establishes the appliance disconnecting means.

  • DWhen the panelboard directory identifies the appliance, regardless of distance or locking capability

    Directory identification is required for panelboard circuits generally, but knowing which breaker feeds the appliance does not prevent someone from closing it while a technician has hands in the equipment.

Why B is correct

The rule gives two acceptable ways to guarantee the servicer controls the energy source: either the device is visible from the appliance, or it can be locked open so nobody restores power while work is underway. Both conditions target the same hazard from different directions.

What this question is testing

This tests the two-part appliance disconnect rule and whether you can distinguish real disconnect control from circuit identification. The same in-sight-or-lockable structure recurs for motors, air conditioning equipment, and heating equipment.

On the job

Attic fans, ceiling heaters, water heaters, and disposals all raise this question during rough-in. Field practice is simple: if the panel is not visible from the equipment, either install a local switch at the appliance or specify a breaker with permanently installed lockout provisions. Note that the locking means must stay attached to the breaker or panel when the lock is off, which rules out the loose lockout devices some technicians carry in a pouch. A local switch is usually cheaper and never gets argued about at inspection.

Memory technique

See it or lock it, otherwise install a switch at the appliance.

Exam tip

In sight or lockable open is a pattern that repeats through the Code. Learn it once and apply it across articles.

Where to look it up

Article 422 Part III, the appliance disconnecting means sections, plus the general lockable-disconnect requirements in Article 110.

5. A kitchen waste disposer is connected with flexible cord and an attachment plug so the unit can be removed for service. What cord length does Article 422 permit for that connection?

  • ABetween 6 inches and 18 inches

    A 6-inch minimum is shorter than any cord length the Code recognizes for this appliance and would not permit the disposer to be lowered from the sink flange for service.

  • Between 18 inches and 36 inches
  • CBetween 3 feet and 6 feet

    The 3-foot to 4-foot range applies to built-in dishwashers and trash compactors, which sit farther from their receptacle. Applying that range to a disposer leaves excess cord where the drain and disposal body can chafe it.

  • DAny length up to 10 feet, provided the receptacle remains accessible

    No cord length in this section is open-ended. Long cords under a sink are the classic setup for a pinched conductor behind a cabinet drawer or trap.

Why B is correct

The disposer cord range of 18 to 36 inches is short enough to prevent excess cord from coiling in the cabinet and long enough to let the unit drop out of the mounting ring for service. It is one condition among several, including the grounding-type plug and an accessible receptacle.

What this question is testing

This checks whether you know the specific cord-and-plug allowances that make an appliance connection legal, and whether you keep the disposer range separate from the dishwasher and compactor range.

On the job

Under a kitchen sink you often have a disposer and a dishwasher sharing the same cabinet, each with a different permitted cord range and its own receptacle rules. Mount the receptacle in the adjacent cabinet or on the side wall so it stays accessible and away from the drain, use the correct kit cord with the strain relief the appliance provides, and keep the plug end out of the wet zone under the trap. Local amendments sometimes address dishwasher receptacle placement, so confirm with the inspector on new construction.

Memory technique

Disposer measures in inches, 18 to 36; dishwasher measures in feet, 3 to 4.

Exam tip

Learn the three appliance cord ranges as a set, since exam questions routinely swap one appliance for another while keeping the same numbers.

Where to look it up

Article 422 Part II, the section on flexible cord connections for specific appliances, with separate paragraphs for disposers, dishwashers, and trash compactors.

6. A single-pole general-use switch is being installed on a 120-volt branch circuit that has one ungrounded conductor and one grounded conductor. How does the Code treat the grounded conductor at that switch?

  • The switch shall open the ungrounded conductor, unless the switching device opens all conductors of the circuit at the same time
  • BThe switch may open either conductor of the circuit, whichever makes the wiring in the box simpler to arrange

    Leaving the choice to the installer is exactly what this rule prevents. Opening only the grounded conductor leaves the load and everything downstream of the switch sitting at line potential.

  • CThe switch shall open the grounded conductor, so that the load is isolated from earth and cannot leak current to ground when the switch is off

    This inverts the rule. Isolating the load from the grounded conductor leaves line voltage on the equipment, which is the hazard a person servicing a luminaire walks into with the switch off.

  • DThe switch may open the grounded conductor wherever the circuit also has ground-fault circuit-interrupter protection

    Ground-fault protection responds to current leaving the circuit. It does nothing about a load that is still connected to the ungrounded conductor after the switch has been opened.

Why A is correct

The requirement is that switching take place in the ungrounded conductor so that opening the switch actually de-energizes the load. A device that opens every circuit conductor at the same moment is acceptable because there is no interval during which the load sits energized through an unswitched ungrounded conductor.

What this question is testing

This checks a foundational safety rule and the way the Code writes its narrow allowance for multipole devices. Candidates who read the allowance as a general permission to switch the grounded conductor pick the wrong answer.

On the job

Older two-wire switch loops and hurried remodels produce switched neutrals more often than anyone likes to admit, and the symptom is a lighting circuit that reads zero volts across the lamp but 120 volts from the shell to a ground rod. Somebody eventually finds it with a knuckle. When a service call reports a tingle from a light fixture that is switched off, a switched grounded conductor is near the top of the list, right alongside a broken grounded conductor upstream.

Memory technique

Switch the hot; the white stays put.

Exam tip

Read the phrase all conductors simultaneously carefully. That is the only door the Code opens for switching a grounded conductor.

Where to look it up

Article 404, the opening sections on switch connections, covering three-way and four-way switching and grounded conductors.

7. A luminaire is being installed in a location the Code classifies as wet. What does the Code require of that luminaire and its installation?

  • It shall be marked as suitable for wet locations, and installed so water cannot enter or accumulate in the wiring compartment, lampholder, or other electrical parts
  • BIt shall be supplied by a circuit protected at not more than 15 amperes and wired with weather-resistant flexible cord terminating in a covered outlet box below the luminaire

    Circuit rating and cord type do nothing to keep water out of a lampholder. The error path answers a construction and marking question with wiring-method details, and an indoor-rated luminaire in the rain is unchanged by the size of its device.

  • CIt shall be mounted at least 8 feet above grade so that rain cannot reach the lens, and aimed downward to shed water from the housing

    Height does not keep water out, since wind-driven rain reaches a fixture at any elevation and a wet location classification does not change with mounting height. The error path treats a wet location as a splash zone near the ground.

  • DIt shall be sealed at the job site with silicone at every housing joint and at each conduit entry before the luminaire is first energized

    Field sealing an indoor-rated housing does not give it a wet-location marking, and it traps the condensation that forms inside. A listed wet-location luminaire is built to drain, which is the opposite of being sealed shut.

Why A is correct

The Code puts the burden on the product marking and on the installation together. The luminaire must carry a marking identifying it as suitable for wet locations, and it must be installed so that water cannot enter or accumulate in wiring compartments, lampholders, or other electrical parts. A damp-location fixture is a lesser rating and does not qualify.

What this question is testing

This tests the pairing of location classification with product marking, a pattern the Code repeats for boxes, receptacles, enclosures, and conductors. Recognizing the pattern lets you answer several questions from one idea.

On the job

The classic failure is a decorative fixture chosen by an owner or designer from a catalog and installed under an open soffit or on an exposed post. It fills with water, the lamp base corrodes, and the ground-fault device on the circuit starts tripping in every rainstorm. Field crews should check the label before hanging the fixture, because once the trim is up and the owner has paid for it, replacing it is a conversation nobody wants. Fixture orientation matters too: many listed wet-location fixtures are only rated when mounted in a specific position.

Memory technique

Wet outside, wet-rated label inside.

Exam tip

When a stem gives you a location classification, your first move is to look for the marking requirement that goes with it.

Where to look it up

Article 410, the early sections on luminaires in specific locations. Confirm which classification applies using the damp and wet location definitions in Article 100.

8. A magnetic across-the-line starter is being selected for a 25-horsepower, 460-volt motor. Under the general rule, how must that controller be rated?

  • Its horsepower rating at the applied voltage shall be at least the horsepower rating of the motor
  • BIts ampere rating shall be at least 250 percent of the motor full-load current

    That percentage belongs to the branch-circuit short-circuit and ground-fault protective device tables, not to controller selection. Controllers are chosen on horsepower at the applied voltage.

  • CIts horsepower rating shall correspond to the locked-rotor code letter marked on the motor nameplate

    The code letter describes starting inrush and is used to look up locked-rotor current. It is not a horsepower rating and cannot be used to select a controller.

  • DIts ampere rating shall equal the ampere rating of the branch-circuit short-circuit protective device

    The protective device is sized well above the motor current to allow starting inrush. Matching a controller to it would badly oversize the contactor and its overload block.

Why A is correct

Controllers are selected on horsepower at the applied voltage, and that rating must not be lower than the motor horsepower. Rating by horsepower rather than amperes builds the switching duty and the inrush withstand into the selection, which a plain ampere rating would not capture.

What this question is testing

This tests whether you know the unit a controller is rated in and that the rating is voltage-specific. It also checks that you do not carry motor protection percentages over into controller selection.

On the job

Undersized starters are one of the more common causes of repeat motor troubles on process equipment. A contactor asked to break more than its rated horsepower welds its tips or erodes them until the motor single-phases, and the symptom that reaches the electrician is a hot motor and a tripping overload, which sends people looking at the motor rather than at the starter. When replacing a failed starter, always check the horsepower rating at the actual system voltage rather than assuming the physical size tells you the rating.

Memory technique

Controllers speak horsepower, at a stated voltage.

Exam tip

Motor questions each have their own basis: horsepower for controllers, table full-load current for conductors, nameplate current for overloads.

Where to look it up

Article 430 Part VII, motor controllers. The horsepower ratings themselves come from the motor full-load current tables at the end of the article.

9. Air-conditioning equipment with a hermetic refrigerant motor-compressor is marked with both a rated-load current and a branch-circuit selection current. Which of those values governs the sizing of the disconnecting means, the conductors, the controller, and the protective devices?

  • AThe rated-load current, because it reflects the compressor running amperes under design conditions

    Rated-load current is the correct basis only when no branch-circuit selection current is marked. Where both appear, using the lower one undersizes every part of the circuit.

  • The branch-circuit selection current, because the Code directs you to use that marked value wherever it appears
  • CThe average of the two marked values, rounded up to the next whole ampere

    Averaging marked values is not a Code method anywhere. The Code always tells you which single marked value to use.

  • DThe locked-rotor current, because it is the largest current the compressor will ever draw

    Locked-rotor current is a momentary starting figure used for selecting certain disconnect types and for short-circuit studies, never for sizing conductors or overload protection.

Why B is correct

A branch-circuit selection current appears on the nameplate when the manufacturer wants the circuit sized above the compressor rated-load current, typically because a protective device inside the unit is set to allow a higher continuous current. When that value is marked, the Code substitutes it for the rated-load current in every sizing step for the circuit and its equipment.

What this question is testing

This tests careful nameplate reading, which is what Article 440 is really about. The exam wants to see whether you know that a branch-circuit selection current, when present, displaces the rated-load current everywhere.

On the job

Rooftop units and heat pumps are usually installed against a nameplate that lists a minimum circuit ampacity and a maximum overcurrent device, which the manufacturer already derived from these rules. Trouble starts when a unit is field assembled or when a compressor is replaced and the installer works from the compressor label alone. Reading the wrong current off a nameplate that carries three of them yields a conductor one or two sizes small and an overcurrent device that nuisance trips on hot afternoons, which is precisely when the equipment is needed.

Memory technique

If a selection current is marked, it wins.

Exam tip

On air-conditioning questions, scan the nameplate data in the stem first and ask which currents are marked. That decides which rule applies before any arithmetic starts.

Where to look it up

Article 440 Part I, the sections covering marking on hermetic motor-compressors and the ampacity and rating provisions that follow.

10. A continuous-duty motor has a marked service factor of 1.15 and a nameplate full-load current of 34 amperes. Its overload device, sized at 125 percent, trips during starting even though the motor is not overloaded. To what maximum may the overload rating be increased?

  • 47.6 amperes
  • B42.5 amperes

    Forty-two and a half amperes is 125 percent, which is where the selection started and which the problem states is already tripping.

  • C44.2 amperes

    One hundred thirty percent is the ceiling for motors that do not carry a service factor of 1.15 or a 40 degree Celsius rise marking. This motor qualifies for the higher ceiling.

  • D51.0 amperes

    One hundred fifty percent exceeds every ceiling in this section. Setting an overload there gives up meaningful thermal protection for the winding.

Why A is correct

Two numbers separate the initial selection from the maximum increase. The initial device is 125 percent of nameplate for this motor class, or 42.5 amperes. Where that proves insufficient, the maximum permitted increase is 140 percent, or 47.6 amperes. The motor class that only qualifies for 115 percent initially is capped at 130 percent on the increase.

What this question is testing

The item tests whether the candidate can distinguish the initial overload selection from the maximum permitted increase, and match the correct ceiling to the motor's nameplate markings.

On the job

Nuisance overload trips on hard-starting loads such as conveyors, compressors, and loaded fans are a daily service call. The wrong response is to jumper the overload or install the largest heater in the drawer. The Code gives a defined ceiling, and if the motor still trips at that ceiling the problem is mechanical, a supply voltage issue, or a genuinely overloaded machine, all of which need investigating rather than a larger heater.

Memory technique

Start at 125, and if it trips you may go to 140. Never past it.

Exam tip

Two ladders in one section: 125 and 115 percent for selection, 140 and 130 percent for the increase. The nameplate decides which rung.

Where to look it up

Look in the motors article, in the overload protection part, at the section on continuous-duty motors and the subsection permitting an increased selection.

11. What does the Code require of a disconnecting means installed for a motor and its controller?

  • AIt must open the grounded conductor along with all of the ungrounded supply conductors

    The grounded conductor is normally not opened by the disconnect. Switching it can leave equipment energized with no return reference and is not what this section requires.

  • BIt must be capable of being operated one pole at a time so a technician can isolate phases

    Independent pole operation is expressly prohibited. Opening one phase of a running three-phase motor is one of the fastest ways to burn its windings.

  • CIt must be located within 6 feet of the motor controller in every installation without exception

    The location rules use in sight from the controller and from the motor, not a fixed 6-foot dimension, and they carry their own exceptions.

  • It must open all ungrounded supply conductors and plainly indicate whether it is open or closed

Why D is correct

Three ideas in one place: all ungrounded conductors open together, no pole operable by itself, and clear indication of position. The grounded conductor is generally not switched. Distance requirements are covered by separate sections on disconnect location, which use the in sight from concept rather than a fixed 6-foot figure.

What this question is testing

The item tests recall of the basic design requirements for a motor disconnect and whether the candidate recognizes single-phasing as the hazard behind the prohibition on independent poles.

On the job

Single phasing from a partially opened disconnect, a blown fuse, or a loose lug is one of the most common causes of motor failure in plants. The disconnect design rules address the part the electrician controls. In the field the practical companions are checking that the handle position indication is legible after painting, and that the switch is not jammed by a locking device that lets it sit between positions.

Memory technique

All the hots at once, and a handle that tells the truth.

Exam tip

Disconnect questions split into two families: what it must do electrically, and where it must be located. Answer the one being asked.

Where to look it up

Look in the motors article, in the part on disconnecting means, at the sections covering what the disconnect must open and how it indicates position.

12. Electric vehicle supply equipment is rated 100 amperes at 208 volts. What does the Code require for its disconnecting means?

  • ANo separate disconnect is required where the branch-circuit breaker is within sight of the equipment and lockable

    In sight of the equipment is not the standard here, and a breaker two floors away in a locked electrical room is neither readily accessible from the charger nor a substitute for the required disconnect.

  • A disconnecting means installed in a readily accessible location and capable of being locked in the open position
  • CA disconnecting means located within 3 feet of the charging equipment enclosure on the same wall

    There is no 3-foot dimension in this requirement. The standard is readily accessible and lockable, which allows considerable flexibility in placement.

  • DA disconnecting means is required only where the equipment exceeds 150 volts to ground

    Voltage to ground is only one of the two triggers. Exceeding 60 amperes brings the requirement into play on its own.

Why B is correct

The trigger is either condition: more than 60 amperes, or more than 150 volts to ground. Meeting one is enough. Once triggered, the disconnect must be readily accessible and lockable in the open position, with the locking means remaining in place with or without the lock installed.

What this question is testing

The item tests whether the candidate can apply a two-part trigger where either condition suffices, and knows the specific attributes the disconnect must have.

On the job

Commercial charging installations are growing fast and are almost always remote from the electrical room, sometimes on a different level of a garage. Without a local lockable disconnect, servicing the unit means coordinating with building staff to find and lock out a breaker somewhere else. The disconnect also matters for emergency responders. On dwelling installations the smaller equipment usually falls below the thresholds and no separate disconnect is required.

Memory technique

Over sixty amperes or over 150 volts to ground: readily accessible and lockable.

Exam tip

When a rule says more than X or more than Y, either one alone triggers it. Do not look for both.

Where to look it up

Look in the electric vehicle power transfer system article, in the part covering equipment construction and installation, at the disconnecting means section.

13. A capacitor bank rated 480 volts is installed for power factor correction. What does the Code require regarding the charge stored in those capacitors?

  • The residual voltage must be reduced to 50 volts or less within 1 minute after disconnection
  • BThe residual voltage must be reduced to zero within 5 minutes after the bank is disconnected

    Zero volts in five minutes is neither the threshold nor the time the Code states, and requiring absolute zero would be unverifiable in practice.

  • CA grounding switch must be closed by the electrician before the enclosure door can be opened

    A manual grounding switch is not permitted as the means of discharge, because it depends on a person doing something before the hazard is removed.

  • DThe terminals must be short circuited with a jumper by the servicing electrician within 15 minutes

    Shorting the terminals by hand is a field practice on high-voltage equipment, not the automatic discharge means the section requires.

Why A is correct

The rule sets a measurable performance requirement: 50 volts or less in one minute for units rated 1000 volts and below. Higher-rated capacitors get a longer allowance. The discharge means must operate automatically, which is why the section also prohibits relying on a manual switching operation to start the discharge.

What this question is testing

The item tests recall of a specific performance requirement expressed as a voltage and a time, and whether the candidate understands why the discharge must be automatic.

On the job

A disconnected capacitor bank can hold a lethal charge, and the person opening the door is often not the one who switched it off. The Code requires the discharge to be automatic for that reason. Field practice still calls for verifying with a meter and grounding the terminals before touching them, because discharge resistors fail open silently and nothing about the enclosure will tell you that it has happened.

Memory technique

Fifty volts in one minute, all by itself.

Exam tip

Capacitor questions almost always turn on stored energy: how much, how fast it drains, and whether draining is automatic.

Where to look it up

Look in the capacitors article at the section covering the drainage of stored charge.

45 more in the bank

Answers and explanations for these are in the app.

  • A motor branch circuit has an overload relay in the starter and an inverse-time circuit breaker in the panelboard. Which statement correctly describes the job of the overload device?
  • Under the general rule of Article 430, where must the disconnecting means for a permanently installed motor be located so a worker servicing the equipment can verify it is open?
  • A continuous-duty 3-phase motor is supplied at 460 volts. The Article 430 motor table lists its full-load current as 14 A, while the nameplate is marked 12.8 A. What is the minimum ampacity required for the branch-circuit conductors supplying this single motor?
  • A continuous-duty motor rated more than 1 horsepower has a nameplate full-load current of 12.8 A and a marked service factor of 1.15. The Article 430 table lists 14 A for that horsepower and voltage. Using the standard percentage for a motor with that service factor, what is the maximum size of the separate running overload device?
  • A 3-phase squirrel-cage motor has an Article 430 table full-load current of 34 A and is protected by an inverse-time circuit breaker. Applying the standard maximum percentage for that device type, and then the allowance to move up when the result falls between standard ratings, what breaker rating is permitted?
  • A feeder supplies three continuous-duty motors whose Article 430 table full-load currents are 28 A, 14 A, and 9.6 A. What is the minimum ampacity the feeder conductors must have for this motor group?
  • A motor circuit rated 1000 volts or less supplies a motor whose Article 430 table full-load current is 34 A. Based on the required percentage of full-load current for a motor circuit disconnecting means, what is the minimum ampere rating that disconnect must have?
  • A transformer rated 1000 volts or less is protected by an overcurrent device on the primary side only, and its primary full-load current is 9 amperes or more. What is the maximum percentage of primary current permitted for that device before the next-standard-rating allowance is applied?
  • A 3-phase transformer steps 480 volts down to 208Y/120 volts and feeds a panelboard several feet away. Which statement correctly describes how the conductors leaving the transformer secondary must be protected?
  • A dry-type transformer rated 112.5 kVA or less is installed indoors close to combustible material. What separation does Article 450 require under the general rule?
  • A surface-mounted LED luminaire with a completely enclosed light source is installed in a clothes closet. What minimum clearance must be maintained between that luminaire and the nearest point of the defined storage space?
  • A ceiling-suspended paddle fan is to be supported solely by the outlet box at that location. What does Article 314 require of that box?
  • A fixed storage-type electric water heater with a capacity of 120 gallons or less is being wired on its own branch circuit. How does the Code treat this load when the branch circuit is sized?
  • A 20-ampere branch circuit supplies several 125-volt receptacle outlets in a dwelling unit. Which receptacle ampere ratings are permitted to be installed on that circuit?
  • Switches control lighting loads in habitable rooms, hallways, and bathrooms that are supplied by a grounded general-purpose branch circuit. Which conductor does Article 404 generally require to be present at each of those switch locations?
  • Flexible cord is connected to a device and to fittings on a piece of utilization equipment. What does the Code require concerning the mechanical tension carried by that cord?
  • A flexible cord contains five current-carrying 12 AWG conductors. The flexible cord ampacity table gives 25 amperes for a 12 AWG conductor in a cord having three or fewer current-carrying conductors, and the adjustment factor for four to six current-carrying conductors is 80 percent. What is the adjusted ampacity of each of those conductors?
  • A general-use switch or a circuit breaker used as a switch is being mounted on a wall. Measured with the operating handle in its highest position, how far above the floor or working platform may the center of the handle grip be?
  • A snap switch is being replaced in a metal box on a wiring system that contains no equipment grounding conductor and provides no metallic path back to the panel. What does the Code permit for that replacement?
  • A non-grounding-type receptacle is being replaced in a dwelling where the branch circuit contains no equipment grounding conductor. Which replacement complies with the Code?
  • Faceplates are being installed on receptacles throughout a finished commercial space. What does the Code require of the way each faceplate fits?
  • A 20-ampere, 125-volt nonlocking receptacle is being installed in a damp or wet location. Beyond the enclosure and cover requirements, what does the Code require of the receptacle itself?
  • Lighting track is being laid out in a retail space. Which of these locations is one where the Code prohibits installing lighting track?
  • The Code lists specific appliances that must be provided with ground-fault circuit-interrupter protection for personnel. Which cord-and-plug-connected appliance appears on that list?
  • Fixed electric space-heating equipment contains heating elements, a motor controller for its fan, and supplementary overcurrent protection inside the cabinet. What must the disconnecting means for that equipment accomplish?
  • A stationary motor rated 1.5 horsepower is cord-and-plug-connected. What is permitted to serve as the disconnecting means for that motor?
  • A disconnecting means is being installed for air-conditioning equipment. Where does the Code require that disconnect to be placed?
  • A hermetic refrigerant motor-compressor has a rated-load current of 24 amperes and no branch-circuit selection current is marked. The Code caps the branch-circuit short-circuit and ground-fault protective device at 175 percent of that current. Standard device ratings available are 20, 25, 30, 35, 40, 45, 50, and 60 amperes. What is the largest standard device rating permitted under that cap?
  • A permanently installed generator supplies loads in a building. What does the Code require regarding a disconnecting means for that generator?
  • A capacitor installed for power factor correction has a rated current of 30 amperes. The Code requires the ampacity of the capacitor circuit conductors to be at least 135 percent of the rated current of the capacitor. What minimum conductor ampacity does that produce?
  • A single-phase transformer rated 1000 volts or less is protected on the primary side only, and its primary full-load current is 6.25 amperes. Where the primary current is at least 2 amperes but less than 9 amperes, the Code caps the primary protective device at 167 percent of the primary current. Standard device ratings available are 6, 10, 15, 20, 25, and 30 amperes. What is the largest standard rating permitted?
  • A 45 kVA three-phase transformer has a 208Y/120-volt secondary whose full-load current is 125 amperes, and it is protected by an overcurrent device on the secondary side. The Code permits that secondary device to be rated at not more than 125 percent of the secondary full-load current, and where 125 percent does not correspond to a standard rating, the next higher standard rating is permitted. Standard ratings include 125, 150, 175, and 200 amperes. What is the maximum permitted secondary device rating?
  • A lay-in luminaire is being installed in the framing members of a suspended ceiling system. What does the Code require to secure it?
  • A transformer is installed in a commercial building. What does the Code require for its disconnecting means?
  • Which installation of a dry-type transformer rated 1000 volts or less does the Code permit without the transformer being readily accessible?
  • A panelboard in a commercial building is supplied by a feeder from an upstream distribution board. What marking does the Code require on that panelboard?
  • An existing receptacle is being replaced in a dwelling laundry area, a location that current requirements would cover, although the circuit feeding it has no such protection today. What does the Code require of the replacement device?
  • A recessed luminaire that is not identified for contact with insulation is installed in a ceiling framed with wood. What clearance does the Code require between the recessed parts of the luminaire and combustible material?
  • A general-use snap switch is being installed on an exterior building wall, which is a wet location. What does the Code require of its enclosure?
  • A panelboard will be supplied by a feeder serving a calculated load. What does the Code require of the panelboard rating?
  • A wall switch is proposed for installation inside the shower space of a dwelling bathroom. How does the Code treat that?
  • Conductors run 8 feet from a transformer secondary to a panelboard, with no overcurrent device at the transformer secondary terminals. Which condition must those conductors satisfy?
  • A wound-rotor motor has a full-load current of 27 amperes from the motor table and will be protected by an inverse-time circuit breaker. The table of maximum ratings permits 150 percent of full-load current for a wound-rotor motor protected by that device type, and where the calculated value does not correspond to a standard rating the next higher standard rating is permitted. What is the largest breaker this motor may use?
  • A squirrel-cage motor with a full-load current of 21 amperes is supplied through a listed combination motor controller whose branch-circuit device is an instantaneous-trip circuit breaker. The table of maximum ratings permits 800 percent of full-load current for that device type on this motor. What is the largest setting permitted for that breaker?
  • Two continuous-duty motors rated more than 1 horsepower each have a nameplate full-load current of 39 amperes. One nameplate carries a service factor of 1.15; the other shows no service factor at all but is marked with a temperature rise of not over 40 degrees Celsius. Separate overload protection is permitted at 125 percent of full-load current for a motor with a service factor of 1.15 or greater or a marked temperature rise of not over 40 degrees Celsius, and at 115 percent for other motors. What maximum overload rating applies to each of these two motors?