Under 2023 NEC 430.6(A), an ordinary single-speed, continuous-duty 1800-RPM motor is covered by the Article 430 current tables. It is not a high-torque motor, canned pump or listed motor-operated appliance, and no nameplate-value exception applies. Which current basis is used for conductor ampacity and branch-circuit short-circuit and ground-fault protection?

Electrician exam practice question · Equipment for General Use

Under 2023 NEC 430.6(A), an ordinary single-speed, continuous-duty 1800-RPM motor is covered by the Article 430 current tables. It is not a high-torque motor, canned pump or listed motor-operated appliance, and no nameplate-value exception applies. Which current basis is used for conductor ampacity and branch-circuit short-circuit and ground-fault protection?

  • AA measured running current alone
  • The applicable Article 430 table full-load current
  • CThe nameplate locked-rotor current
  • DThe nameplate full-load current instead of the table value

Where to look it up

https://captaincode2023.leviton.com/node/346

Why B is correct

For this stated general application, use the applicable table current. Nameplate current is used for separate overload protection, but that is not its only possible use: 430.6 also specifies nameplate treatment for particular motors and exceptions. A measured operating current is not the table basis. This question selects the current source; sizing factors and other installation conditions must still be applied separately. Source: https://captaincode2023.leviton.com/node/346