1. Apply the 2023 NEC including issued TIA 23-17. A permanently installed swimming-pool pump motor is supplied by a 120-volt-to-ground, single-phase, 20-ampere branch circuit and does not qualify for the listed low-voltage exception. What ground-fault protection is required for the outlet supplying it, including a direct-wired connection?
- AArc-fault protection alone at the panelboard
- Class A GFCI protection
- CA surge protective device instead of ground-fault protection
- DAn isolated equipment grounding conductor instead of ground-fault protection
Where to look it up
https://docinfofiles.nfpa.org/files/AboutTheCodes/70/FD_D25_1_SC_25-4_6_d_TIA_1809_NFPA_70.pdf
Why B is correct
TIA 23-17 revises 680.21(C) to require ground-fault protection for outlets serving pool motors, subject to its stated low-voltage exception. For the specified 120 V-to-ground, 20 A single-phase circuit, 680.5(B) calls for a Class A GFCI. Direct wiring does not remove the outlet requirement. The amended rule should not be summarized as applying only to 15 A or 20 A pump circuits. Sources: issued TIA 23-17, effective April 30, 2025, PDF page 3: https://docinfofiles.nfpa.org/files/AboutTheCodes/70/FD_D25_1_SC_25-4_6_d_TIA_1809_NFPA_70.pdf; 2023 baseline 680.5(B), NFPA Public Input 4500, PDF page 364 (printed 117): https://docinfofiles.nfpa.org/files/AboutTheCodes/70/70_A2025_NEC_P17_FD_PIResponses.pdf