EstatePass

HVACNHIE Practice Questions

140 questions in this content area. 23 are published in full below with worked explanations.

1. A baseboard hydronic heater with crushed fins delivers less heat because:

  • AThe damage causes air to enter the system
  • BThe crushed section restricts water flow through the pipe
  • Bent fins reduce the surface area transferring heat
  • DThe fins carry the water rather than the pipe

Why C is correct

Why this is correct: The fins on a baseboard heater are designed to increase the surface area of the hot water pipe, maximizing heat transfer to the room air. Crushing the fins dramatically reduces this surface area, so less heat is transferred even though the water inside the pipe remains hot. Why the other choices are wrong: 'The damage causes air to enter the system' is wrong; crushed fins are external and do not affect the sealed hydronic loop. 'The crushed section restricts water flow through the pipe' is wrong; the internal pipe diameter is typically unaffected by external fin damage. 'The fins carry the water rather than the pipe' is wrong; water flows only inside the pipe, not the fins. Exam tip: Fins = surface area. Damaged fins = less surface area = less heat output.

2. A high-efficiency condensing furnace is distinguished by:

  • AThe absence of any electrical connections
  • BA metal chimney connector serving the appliance directly
  • PVC intake and exhaust piping and a condensate drain
  • DA pilot light that burns continuously all year

Why C is correct

Why this is correct: A high-efficiency condensing furnace is distinguished by PVC intake and exhaust piping and a condensate drain. The condensing process extracts so much heat that exhaust gases cool enough to be vented safely through plastic (PVC) pipes. This process also creates acidic condensate that must be drained away, requiring a dedicated drain line. Why the other choices are wrong: The absence of any electrical connections is wrong; these furnaces require electrical power for controls and blowers. A metal chimney connector serving the appliance directly is typical of standard-efficiency furnaces with hot exhaust, not condensing models. A pilot light that burns continuously all year describes a standing pilot, not a feature of modern high-efficiency condensing furnaces. Exam tip: Look for the white plastic (PVC) pipes and a condensate drain line—these are the visual hallmarks of a condensing furnace.

3. A return air opening is located inside a closet containing a gas water heater. Why is this reported?

  • Return air must not be drawn from such a space
  • BThe closet is too small to supply enough air
  • CReturn openings must always be near the floor
  • DThe water heater will restrict the airflow

Why A is correct

Why this is correct: Return air must not be drawn from a closet containing a fuel-burning appliance (like a gas water heater). The return duct creates negative pressure (depressurization) in that closet. This can interfere with the appliance's draft, potentially pulling combustion products (like carbon monoxide) back into the closet and then distributing them throughout the home via the duct system. Why the other choices are wrong: The closet is too small to supply enough air is not the primary code/safety reason. Return openings must always be near the floor is false; they can be high or low. The water heater will restrict the airflow is a minor concern compared to the combustion gas hazard. Exam tip: Returns cannot be in rooms with fuel-burning appliances due to backdraft risk.

4. A room has a supply register but no return path when its door is closed. What follows?

  • The room becomes pressurised and airflow drops
  • BThe room will be quieter than adjacent spaces
  • CThe furnace filter will load more slowly
  • DThe room will draw air from the attic space

Why A is correct

Why this is correct: The room becomes pressurised and airflow drops. The governing principle is air balance. An HVAC system requires a return path for air to leave a room. With a closed door and no return or transfer path, supply air pressurizes the room. This positive pressure opposes the blower, reducing or stopping further airflow from the supply register. Why the other choices are wrong: The room will be quieter than adjacent spaces is not necessarily true. The furnace filter will load more slowly is incorrect; reduced airflow might actually cause more debris to bypass the filter. The room will draw air from the attic space is possible but is a secondary effect of depressurization, not pressurization. Exam tip: For rooms with a closed door, check for an undercut door (1-inch gap), transfer grille, or dedicated return duct to ensure proper airflow.

5. An emergency shutoff switch for the furnace is found inside the furnace room beside the unit. Why is placement reported?

  • AThe switch will be damaged by heat in that position
  • Reaching it may require entering a hazardous area
  • CThe switch must be located outside the building
  • DSwitches inside a room cannot be labelled clearly

Why B is correct

Why this is correct: An emergency shutoff switch must allow safe power cutoff without approaching a hazardous appliance, especially during a fire or smoke event. Placing it inside the furnace room defeats its purpose because reaching it requires entering the potentially dangerous area it is meant to avoid. Why the other choices are wrong: "The switch will be damaged by heat in that position" is incorrect because proximity to the unit alone does not inherently cause damage; switches are rated for such environments. "The switch must be located outside the building" is wrong; codes typically require it outside the furnace room, not necessarily outside the building. "Switches inside a room cannot be labelled clearly" is false; labeling is possible regardless of location. Exam tip: Remember: emergency shutoffs should be accessible without entering the hazard zone—usually outside the furnace room.

6. Duct in a crawl space rests directly on the soil. What should the report note?

  • AThe duct will be more efficient in contact with earth
  • Soil contact promotes corrosion and moisture entry
  • CThe duct requires no support if soil-bearing
  • DSoil contact improves the duct's insulation value

Why B is correct

Why this is correct: The governing concept is that ductwork should be protected from ground moisture. Soil contact promotes rust in metal ducts, saturates insulation on flexible ducts, and can allow soil gases and moisture to enter the air stream through leaks. Why the other choices are wrong: 'The duct will be more efficient in contact with earth' is wrong; earth contact increases heat loss/gain and moisture problems, reducing efficiency. 'The duct requires no support if soil-bearing' is wrong; ducts should be supported off the ground, not resting on soil. 'Soil contact improves the duct's insulation value' is wrong; wet insulation loses its insulating value. Exam tip: Duct on dirt = moisture and corrosion problem. It should be suspended.

7. Flexible ducts sagging between supports in an attic reduce performance because:

  • ASagging ducts leak more air at their seams
  • BThe duct's insulation value drops when it sags
  • Sags create turbulence and effective length, cutting flow
  • DThe sag noticeably changes the air's temperature in transit

Why C is correct

Why this is correct: Flexible duct is designed to be installed fully extended and supported. Sagging creates kinks and dips that increase turbulence and air resistance (friction), effectively increasing the duct's 'equivalent length.' This increased static pressure reduces airflow (CFM) to the register, cutting system performance, as the original explanation states. Why the other choices are wrong: 'Sagging ducts leak more air at their seams' is wrong; while possible, the primary performance issue with sagging is increased resistance, not necessarily increased leakage. 'The duct's insulation value drops when it sags' is wrong; the R-value of the insulation batt is largely unaffected by sagging. 'The sag noticeably changes the air's temperature in transit' is wrong; temperature change is minimal and not the primary performance issue. Exam tip: For ductwork, think 'airflow.' Any restriction (sag, kink, crush) increases resistance and reduces delivered CFM.

8. Return air taken from a garage or a mechanical closet containing fuel-burning appliances is a concern because:

  • AIt causes the filter to load more slowly
  • BIt reduces the system's cooling capacity slightly
  • CIt makes the ductwork harder to clean
  • It can draw combustion products into the living space

Why D is correct

Why this is correct: Return ducts are under negative pressure (suction). A return grill in a garage or mechanical closet will draw in surrounding air, which can contain carbon monoxide, fuel fumes, or other hazardous combustion byproducts from appliances. This contaminated air is then distributed throughout the living space, creating a serious health and safety hazard, as the original explanation emphasizes. Why the other choices are wrong: 'It causes the filter to load more slowly' is wrong; this is a trivial effect and not the core safety concern. 'It reduces the system's cooling capacity slightly' is wrong; while possible, capacity impact is secondary to the life safety issue. 'It makes the ductwork harder to clean' is wrong; this is not a relevant or primary concern for this configuration. Exam tip: Return air from garages, workshops, or furnace rooms is a critical safety defect due to risk of carbon monoxide poisoning.

9. Rust flakes and scaling are found inside a furnace burner compartment. What should the inspector consider?

  • Moisture has been reaching the compartment
  • BThe burners were installed at the wrong angle
  • CThe furnace has been operated at low fire only
  • DThe filter was changed too frequently

Why A is correct

Why this is correct: Moisture has been reaching the compartment. The governing concept is that rust (iron oxide) requires the presence of water or moisture. A dry, properly operating furnace burner compartment should not have significant rust or scaling. Its presence indicates an abnormal moisture source, such as condensation from poor combustion, a flue leak, or an external water leak. Why the other choices are wrong: The burners were installed at the wrong angle would not cause rust. The furnace has been operated at low fire only might cause sooting, not necessarily rust. The filter was changed too frequently is unrelated to rust formation inside the burner compartment. Exam tip: Rust inside a furnace = unwanted moisture. Trace the source, as it can indicate serious venting or heat exchanger issues.

10. Two gas appliances vented into a common flue with the smaller connector entering below the larger is:

  • AA near guarantee that both of the appliances will backdraft
  • BAlways prohibited under every circumstance
  • CAcceptable only when both appliances are new
  • A conventional arrangement, provided sizing is correct

Why D is correct

Why this is correct: A conventional arrangement, provided sizing is correct. The governing concept is that common venting of gas appliances is a permitted and common practice when installed correctly. Key requirements include proper sizing of the common flue for the combined appliance input and correct connection order (typically the larger appliance connector enters higher). The inspector checks for proper draft and spillage, not the mere presence of common venting. Why the other choices are wrong: 'A near guarantee that both of the appliances will backdraft' is wrong; a properly sized and installed common vent does not guarantee backdrafting. 'Always prohibited under every circumstance' is wrong; codes permit common venting. 'Acceptable only when both appliances are new' is wrong; the age of appliances is not the determining factor for common venting acceptability. Exam tip: Common venting is not inherently defective; look for evidence of improper operation (spillage) or undersizing.

11. Vegetation has grown tightly around an outdoor condensing unit. What is the concern?

  • ARoots will disturb the unit's mounting pad
  • BLeaves will enter the refrigerant circuit
  • Restricted airflow reduces the unit's ability to reject heat
  • DThe unit will be difficult to read for billing

Why C is correct

Why this is correct: Restricted airflow reduces the unit's ability to reject heat. The condenser coil needs unimpeded airflow to release the heat absorbed from inside the home. Vegetation blocking the coil reduces airflow, causing the system to run less efficiently (higher head pressure), work harder, and potentially overheat, leading to premature failure. Why the other choices are wrong: Roots will disturb the unit's mounting pad is possible but not the primary immediate concern. Leaves will enter the refrigerant circuit is impossible; the circuit is a sealed system. The unit will be difficult to read for billing is trivial and not a mechanical concern. Exam tip: Keep plants at least 2-3 feet clear around the condenser for proper airflow. This is a simple but important maintenance item.

12. What does an inspector note about vent connectors secured with sheet metal screws?

  • AScrews are prohibited on vent connectors
  • BScrews indicate the connector is undersized
  • Screws prevent the joints from separating
  • DScrews must be removed before servicing

Why C is correct

Why this is correct: Vent connectors (the pipe between the appliance and the chimney or main vent) experience thermal expansion and vibration. Sheet metal screws at each joint (usually 3 screws spaced evenly) are the proper method to secure the sections and prevent them from separating. Why the other choices are wrong: 'Screws are prohibited on vent connectors' is the opposite of the truth; they are required. 'Screws indicate the connector is undersized' is incorrect; sizing is separate from fastening. 'Screws must be removed before servicing' is false; they are permanent fasteners. Exam tip: Proper vent connector assembly: screws at every joint, not tape.

13. What does an inspector observe about a boiler's relief valve discharge piping?

  • AThat it is threaded to accept a cap
  • BThat it connects to the domestic hot water line
  • CThat it rises above the boiler before terminating
  • That it terminates safely and is not obstructed

Why D is correct

Why this is correct: The Temperature and Pressure Relief (TPR) valve is a critical safety device. Its discharge pipe must terminate in a safe location (e.g., near the floor), be unobstructed, and drain freely to prevent injury from scalding water or steam if the valve opens. Why the other choices are wrong: 'That it is threaded to accept a cap' is dangerous; a cap must never be installed. 'That it connects to the domestic hot water line' is incorrect and would contaminate potable water. 'That it rises above the boiler before terminating' is wrong; it should generally drain downward. Exam tip: TPR valve discharge: safe termination, no valve, no cap, drains freely.

14. What does an inspector observe about an oil storage tank serving a furnace?

  • AIts precise remaining volume in gallons
  • BWhether the tank meets the current wall thickness
  • CThe refining origin of the fuel it contains
  • Its condition, support and any evidence of leakage

Why D is correct

Why this is correct: The governing concept is that inspectors assess oil storage tanks for condition, support, and leakage evidence, as these indicate safety and functionality. The supplied explanation states that tanks corrode internally and fail at the bottom, so staining beneath them is a key observation. Why the other choices are wrong: "Its precise remaining volume in gallons" is wrong because inspectors estimate but do not measure precise volume. "Whether the tank meets the current wall thickness" is wrong because wall thickness cannot be determined visually during an inspection. "The refining origin of the fuel it contains" is wrong because fuel origin is irrelevant to the inspection. Exam tip: Focus on visible condition, support, and leakage signs for oil tanks—not measurements or specifications.

15. What is the function of a limit switch on a forced-air furnace?

  • It shuts the burner down if temperatures rise too high
  • BIt limits how many hours the furnace may run daily
  • CIt restricts the gas pressure delivered to the burner
  • DIt caps the speed at which the blower may operate

Why A is correct

Why this is correct: A limit switch is a safety device that shuts off the furnace burner if the heat exchanger temperature becomes excessively high, usually due to restricted airflow (e.g., clogged filter or blocked ducts). This prevents overheating and potential fire hazards. Why the other choices are wrong: "It limits how many hours the furnace may run daily" is incorrect; that function is handled by a timer or thermostat, not a limit switch. "It restricts the gas pressure delivered to the burner" is wrong; gas pressure is regulated by a gas valve. "It caps the speed at which the blower may operate" is false; blower speed is controlled by a motor or control board. Exam tip: Frequent limit switch trips often indicate airflow problems—check filters and ducts.

16. Why does a cooling system need a condensate drain?

  • ATo remove refrigerant that escapes the coil
  • BTo supply humidity to the conditioned space
  • CTo relieve pressure built up in the system
  • To carry away water condensed from the air

Why D is correct

Why this is correct: As warm, humid indoor air passes over the cold evaporator coil, its temperature drops below the dew point, causing moisture in the air to condense into liquid water. The condensate drain's sole purpose is to collect and channel this water away from the equipment to prevent overflow and water damage. Why the other choices are wrong: To remove refrigerant that escapes the coil is incorrect; refrigerant is contained in sealed coils. To supply humidity to the conditioned space is the opposite of its function. To relieve pressure built up in the system is the function of pressure relief valves, not the condensate drain. Exam tip: Cooling removes humidity; the water that results must be drained away.

17. Why does a general inspection stop short of confirming a heat exchanger is intact?

  • AHeat exchangers never fail in residential furnaces
  • Most of the exchanger is not visible without dismantling
  • COnly the utility may examine a heat exchanger
  • DThe exchanger is excluded from all inspections

Why B is correct

Why this is correct: Most of the exchanger is not visible without dismantling. The governing concept is the scope and limitations of a visual inspection. The heat exchanger is a sealed metal chamber inside the furnace cabinet. Only small portions may be visible through access openings; the vast majority is hidden from view. Therefore, an inspector cannot confirm its overall integrity. Why the other choices are wrong: Heat exchangers never fail in residential furnaces is false; they can and do fail. Only the utility may examine a heat exchanger is incorrect; HVAC technicians can inspect them. The exchanger is excluded from all inspections is an overstatement; inspectors report on visible condition and indirect evidence. Exam tip: You can't inspect what you can't see. For heat exchangers, report visible clues (rust, cracks, soot) and recommend professional evaluation.

18. Why does an inspector check that supply registers are present in each conditioned room?

  • ARegister count determines the system's efficiency rating
  • BRegisters are required to be evenly sized throughout
  • A room without supply air will not be conditioned
  • DRegisters must match the flooring in each room

Why C is correct

Why this is correct: The heating/cooling system's purpose is to condition the air in habitable rooms. A supply register (and a return path) is necessary to deliver conditioned air to that space. A room without a supply register will not receive adequate conditioned air from the central system. Why the other choices are wrong: Register count determines the system's efficiency rating is false; design determines efficiency. Registers are required to be evenly sized throughout is false; sizing varies by room load. Registers must match the flooring in each room is an aesthetic concern, not a functional requirement. Exam tip: Check that all finished, habitable rooms have a supply register to receive conditioned air.

19. Why does an inspector note refrigerant lines that pass through a wall without a sleeve or seal?

  • AThe lines will lose refrigerant at the penetration
  • Unsealed penetrations admit air, water and pests
  • CThe lines must be accessible along their length
  • DSleeves are required to support the line's weight

Why B is correct

Why this is correct: Any penetration in the building envelope should be sealed to prevent air infiltration, water intrusion, and pest entry. Refrigerant lines vibrate, which can enlarge an unsealed hole over time, exacerbating these problems. Why the other choices are wrong: 'The lines will lose refrigerant at the penetration' is false; refrigerant loss requires a leak in the sealed tubing. 'The lines must be accessible along their length' is not a standard requirement for this scenario. 'Sleeves are required to support the line's weight' is incorrect; support is provided by hangers, not sleeves. Exam tip: Treat any penetration through exterior walls the same: it must be sealed.

20. Why does an inspector note the age of a furnace alongside its condition?

  • AAge determines whether the unit may remain in service
  • Condition alone cannot predict a failure date
  • CAge establishes the required flue diameter
  • DOlder units are always less safe than newer ones

Why B is correct

Why this is correct: The core inspection principle is to report observable facts, not predict the future. A furnace's condition (e.g., clean vs. neglected) and its age are two independent data points. Reporting both gives the client a complete picture, but neither fact alone reliably indicates when the unit will fail. Why the other choices are wrong: "Age determines whether the unit may remain in service" is wrong because age alone is not a pass/fail criterion; a well-maintained older unit can be functional. "Age establishes the required flue diameter" is wrong because flue sizing is based on appliance input, not age. "Older units are always less safe than newer ones" is wrong as a blanket statement; safety depends on condition and maintenance, not just age. Exam tip: Remember the inspector's role: report observed conditions and facts, not make definitive predictions about service life.

21. Why does an inspector note whether a furnace's return and supply plenums are sealed at the cabinet?

  • AUnsealed plenums reduce the flue's draft
  • BSealing determines the cabinet's fire rating
  • Leakage moves unconditioned air and wastes capacity
  • DSealing is required for the unit's warranty

Why C is correct

Why this is correct: The furnace cabinet should be airtight where the ductwork connects. Leaks allow the blower to pull in unconditioned air (e.g., from a crawlspace or garage) into the supply, or to lose conditioned air into those spaces, reducing system efficiency and capacity. Why the other choices are wrong: 'Unsealed plenums reduce the flue's draft' is not directly related; draft is affected by the venting system. 'Sealing determines the cabinet's fire rating' is incorrect; the cabinet's fire rating is a separate construction feature. 'Sealing is required for the unit's warranty' may be true, but the core inspection issue is performance and safety. Exam tip: Air leakage at the cabinet wastes energy and can introduce contaminants.

22. Why does an inspector observe supply registers in every room rather than sampling one?

  • ARegisters must be counted for the report
  • BRegister style indicates the duct material
  • CEach register requires individual testing
  • Rooms without supply reveal distribution gaps

Why D is correct

Why this is correct: A complete walk-through ensures every habitable room has a conditioned air supply. Omissions are common in additions or finished spaces where ductwork was not extended. A room without a supply register will have comfort issues and indicates an incomplete system. Why the other choices are wrong: "Registers must be counted for the report" is not a primary reason; counting alone doesn't assess distribution. "Register style indicates the duct material" is unreliable; style and material are not strictly linked. "Each register requires individual testing" is excessive; a sample of airflow is often sufficient. Exam tip: Check every room. Missing supplies in finished spaces are a common defect and explain comfort complaints.

23. Why does an inspector operate a system through its normal controls rather than at the equipment?

  • AEquipment controls are always locked by the manufacturer
  • BThe standard prohibits touching the equipment
  • It tests the path an occupant would actually use
  • DEquipment controls give more accurate readings

Why C is correct

Why this is correct: The purpose is to test the complete operational chain—thermostat, wiring, relays, and equipment—as a homeowner would. If the system only works when jumped at the equipment, the occupant cannot control it, which is a functional failure. Why the other choices are wrong: "Equipment controls are always locked by the manufacturer" is false; many have accessible service switches. "The standard prohibits touching the equipment" is incorrect; inspectors operate systems within safe limits. "Equipment controls give more accurate readings" is wrong; testing at the equipment bypasses the control path, which is the point of inspection. Exam tip: Think like a homeowner. The test is for normal usability, not just technical function.

117 more HVAC questions

Answers and explanations for these are in the study app.

  • A boiler's expansion tank that has become waterlogged will cause:
  • A boiler's relief valve discharges regularly. What should the inspector consider?
  • A building cavity has been used as a return air path rather than sheet metal duct. What is the concern?
  • A condensate drain line from an attic air handler discharges into the attic itself. Why is this reported?
  • A furnace filter is found heavily clogged. Beyond reduced airflow, what should the inspector consider?
  • A furnace filter that has never been changed and is coated with dust affects the system by:
  • A furnace is installed in a small closet with no openings for combustion air. What is the concern?
  • A furnace located in an unconditioned attic requires:
  • A furnace short-cycles, running briefly and shutting off repeatedly. What should be examined first?
  • A furnace's condensate drain line that is clogged will typically cause:
  • A furnace's flame rolls out of the burner compartment when the blower starts. This suggests:
  • A heat pump in heating mode that never enters defrost during freezing weather will:
  • A high-efficiency furnace vents through a plastic pipe in a sidewall. What does this indicate about its combustion?
  • A programmable thermostat wired without a common wire may:
  • A single-wall vent connector passes through a wall into a chimney. What should be examined?
  • A single-wall vent connector passing too close to combustible framing is a concern because:
  • A thermostat is mounted on a wall directly above a supply register. What is the effect?
  • A thermostat is wired for a system feature the equipment does not have. What is the likely consequence?
  • A thermostat's heat anticipator or cycle rate setting affects:
  • A Type B vent passes through a framed ceiling with insulation packed tight against it. What clearance applies?
  • A vent connector has been repaired with duct tape at a joint. Why is this reported?
  • A vent connector with a hole rusted through it should be reported because:
  • A window air conditioner installed in a bedroom's only egress window is:
  • Air trapped in a hot water heating system typically shows as:
  • An air conditioner's evaporator coil that is inaccessible for viewing should be reported as:
  • An air conditioner's outdoor coil packed with cottonwood seed and grass clippings will:
  • An air handler in an attic has a secondary drain pan with no visible drain or switch. Why does this matter?
  • An appliance vent has been extended with a section of a different material. Why is this reported?
  • An inspector finds the insulation missing from the larger refrigerant line at the outdoor unit. What is the effect?
  • An outdoor unit is installed noticeably out of level. Why is this noted?
  • Combustion air for a furnace in a small sealed mechanical room must:
  • Duct joints sealed with cloth-backed duct tape typically:
  • Ductwork in an unconditioned attic is found with joints unsealed. What is the consequence?
  • Flames lift away from the burner and roll toward the front of the furnace when it starts. What does this suggest?
  • Flexible duct in a crawl space is compressed sharply where it passes a beam. What is the effect?
  • How should an inspector operate a heating system during an inspection?
  • Ice is observed on the refrigerant line at an indoor coil during operation. What does this suggest?
  • Radiators in one part of a house stay cold while others heat normally. What should be examined first?
  • Refrigerant line insulation missing on the large suction line causes:
  • Rust and staining are found at the draft hood of a gas furnace. What does this suggest?
  • Soot deposits are found on and around a furnace cabinet. What does this indicate?
  • Soot deposits are visible around a gas burner compartment. What does this indicate?
  • Supply ducts run through an unconditioned attic with no insulation. What is the consequence?
  • The refrigerant suction line at an outdoor unit is bare where its insulation has degraded. Why is this reported?
  • Two furnace vent connectors joined with the connections taped rather than screwed are a concern because:
  • Two gas appliances vent into a shared masonry chimney with no liner. What should the inspector consider?
  • What distinguishes a direct-vent appliance from a conventionally vented one?
  • What does a rusted or wet condensate trap on a high-efficiency furnace suggest?
  • What does a temperature split measured across an evaporator coil indicate?
  • What does an inspector consider when a very dense filter has been fitted to an older system?
  • What does an inspector consider when an outdoor unit is much newer than the indoor coil?
  • What does an inspector do when a system does not respond to its normal controls?
  • What does an inspector examine about a condensing unit's location outdoors?
  • What does an inspector explain about an evaporative cooler serving a house?
  • What does an inspector look for at hydronic radiators and baseboard units?
  • What does an inspector look for at the base of a masonry chimney serving an appliance?
  • What does an inspector note about an electric air handler's heating elements?
  • What does an inspector note when combustion air openings have been sealed by an owner?
  • What does an inspector observe about a furnace's blower compartment door switch?
  • What does an inspector observe about a mini-split's refrigerant line set on an exterior wall?
  • What does an inspector observe about a system with zone valves or multiple thermostats?
  • What does an inspector observe about dampers found in a duct system?
  • What does an inspector report when equipment in a crawl space cannot be reached?
  • What does persistent condensation on windows during heating season suggest?
  • What is happening when a heat pump's outdoor unit briefly blows cool air and steams in winter?
  • What is the limitation of comparing supply and return air temperatures at the registers?
  • What is the purpose of a low-water cutoff on a boiler?
  • What is the purpose of an expansion tank on a hydronic heating system?
  • What is the purpose of auxiliary or emergency heat on a heat pump system?
  • Which location is a permissible source of return air?
  • Why are bleed valves fitted at the high points of a hydronic system?
  • Why does a vent connector need to rise continuously toward the chimney or vent?
  • Why does an inspector allow a system to run for a period rather than confirming it starts?
  • Why does an inspector check the furnace filter even though replacing it is routine maintenance?
  • Why does an inspector check whether a heat pump switches into its heating mode?
  • Why does an inspector decline to operate a cooling system in cold weather?
  • Why does an inspector locate the emergency shutoff switch for a heating system?
  • Why does an inspector look at where a sidewall vent terminates relative to windows and walkways?
  • Why does an inspector look for a vent that has been disconnected at a joint?
  • Why does an inspector look for return air ducts drawing from a garage?
  • Why does an inspector note a bypass humidifier whose damper is left open in summer?
  • Why does an inspector note a chimney that serves both a furnace and a fireplace?
  • Why does an inspector note a condensate pump serving a cooling coil?
  • Why does an inspector note a cooling system that has no visible service history or data plate?
  • Why does an inspector note a filter slot left open at the air handler?
  • Why does an inspector note a flexible gas connector passing through a wall or cabinet?
  • Why does an inspector note a fuel-burning appliance installed in a small closet?
  • Why does an inspector note a furnace in a garage that has no barrier in front of it?
  • Why does an inspector note a furnace installed in a confined space with no transfer openings?
  • Why does an inspector note a furnace that has been installed on its side or in an unusual orientation?
  • Why does an inspector note a heavily loaded air filter?
  • Why does an inspector note a range hood that recirculates rather than discharging outdoors?
  • Why does an inspector note a thermostat located on an exterior wall?
  • Why does an inspector note ductwork that has been disconnected and left in place?
  • Why does an inspector note evidence of past leakage at a boiler even when it is dry?
  • Why does an inspector note excessive rust or debris in a furnace's combustion area?
  • Why does an inspector note flexible duct with long unsupported spans?
  • Why does an inspector note radiators or baseboard units that have been enclosed or covered?
  • Why does an inspector note soot deposits around an oil-fired appliance?
  • Why does an inspector note staining or corrosion around boiler piping connections?
  • Why does an inspector note supply registers that have been closed off in unused rooms?
  • Why does an inspector note the absence of a filter or an ill-fitting filter slot?
  • Why does an inspector note the age of a cooling system relative to its refrigerant type?
  • Why does an inspector note the condition of the outdoor unit's electrical disconnect?
  • Why does an inspector note the height of a vent termination above a flat roof surface?
  • Why does an inspector note the presence and location of carbon monoxide alarms?
  • Why does an inspector note the temperature and pressure gauge reading on a boiler?
  • Why does an inspector note the walkway and lighting serving equipment in an attic?
  • Why does an inspector note where a ductless mini-split's condensate line terminates?
  • Why does an inspector note whether a heat pump's supplemental electric heat operates?
  • Why does an inspector note whether a whole-house fan has an insulated cover for winter?
  • Why does an inspector observe the burner flame colour on a gas furnace where visible?
  • Why does an inspector operate a heat pump in both heating and cooling where conditions permit?
  • Why does an inspector report a heat pump that runs on auxiliary heat during mild weather?
  • Why is a cracked heat exchanger treated as a serious finding?
  • Why is air conditioning not operated when the outdoor temperature is well below normal?
  • Why is duct sealed with cloth-backed adhesive tape a finding worth reporting?
Unlock all 140 questions