You're installing a 100-amp subpanel in a detached garage 80 feet from the main panel. Using 75°C copper conductors in underground conduit, what minimum wire size is required for the feeder conductors?

Correct Answer

C) #1/0 AWG

For 100-amp feeder, #3 AWG copper is normally adequate, but with 80-foot run, voltage drop calculations require upsizing to #1/0 AWG to maintain voltage within acceptable limits.

Answer Options
A
#1 AWG
B
#2/0 AWG
C
#1/0 AWG
D
#2 AWG

Why This Is the Correct Answer

#1/0 AWG copper at 75°C is rated for 150 amps, which provides the necessary capacity for a 100-amp feeder. More importantly, an 80-foot run causes significant voltage drop; the NEC recommends keeping voltage drop to 3% or less for feeders. At 100 amps over 80 feet, a smaller conductor like #2 or #1 AWG would exceed that limit, requiring an upsize to #1/0 AWG to maintain acceptable voltage levels.

Why the Other Options Are Wrong

Option A: #1 AWG

#1 AWG copper at 75°C is rated for 130 amps, which meets ampacity requirements, but the 80-foot run causes too much voltage drop with this gauge. It is close but insufficient once voltage drop is calculated for this distance.

Option B: #2/0 AWG

#2/0 AWG is oversized for this application. While it would work electrically, it is not the minimum required size — the question asks for the minimum. #1/0 AWG satisfies both ampacity and voltage drop requirements without over-engineering.

Option D: #2 AWG

#2 AWG copper at 75°C is rated for 95 amps, which is below the 100-amp breaker rating and fails to meet ampacity requirements. It also produces unacceptable voltage drop over 80 feet at 100 amps.

Memory Technique

For long runs, think 'distance demands more wire.' When distance doubles the normal run, bump up the wire size. For a 100A feeder: normal would be #4 AWG, but 80 feet pushes you up to #1/0 AWG.

Was this explanation helpful?

More Michigan Questions

A residential foundation wall in Michigan is 8 feet high with 2 feet above grade. The backfill exerts lateral pressure of 30 psf per foot of depth. What is the maximum lateral pressure at the bottom of the foundation wall?

A builder discovers that the electrical service entrance was installed without proper permits. According to Michigan law, what is the most appropriate next step?

What is the maximum allowable span for a 2x8 floor joist (Grade 2 Douglas Fir) at 16" O.C. with 40 psf live load and 10 psf dead load according to Michigan Building Code span tables?

According to Michigan Building Code, what is the maximum height of a wood-framed bearing wall using 2x4 studs with standard construction?

A homeowner requests to convert a bedroom into a bathroom on the second floor. What is the primary Michigan code concern the builder must address?

According to Michigan plumbing regulations, what is the minimum pipe size required for a water service line serving a single-family residence?

A contractor is building a basement foundation wall that is 8 feet high and will retain 6 feet of soil. What is the minimum wall thickness required by the Michigan Building Code for poured concrete?

A homeowner wants to install a gas fireplace in their living room. The contractor notices the existing gas line is 1/2 inch black iron pipe. For a 40,000 BTU fireplace with a 25-foot run, is this pipe size adequate according to Michigan gas code?

During a framing inspection, the building official notes that the contractor used 2x4 studs at 24 inches on center for an exterior wall. According to Michigan Building Code, what is the maximum wall height allowed for this configuration?

A contractor is installing a beam to support floor joists. The beam must carry a total load of 8,000 pounds over a 12-foot span. If the allowable fiber stress for the lumber grade is 1,200 psi, what is the minimum required section modulus?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.