During a residential inspection in Michigan, you discover that the contractor installed 2x8 floor joists at 24 inches on center spanning 12 feet. The building official questions whether this meets code requirements for a 40 psf live load. What should be your primary concern?

Correct Answer

A) Both spacing and span exceed recommended limits

2x8 joists at 24" o.c. spanning 12 feet exceeds the recommended span limits for 40 psf live load. The combination of wide spacing and long span creates structural concerns.

Answer Options
A
Both spacing and span exceed recommended limits
B
The joist depth is insufficient for the load
C
The spacing is too wide for the span length
D
The span is acceptable for the joist size

Why This Is the Correct Answer

The primary concern is that BOTH the spacing (24 inches on center) and the span (12 feet) together exceed recommended limits for 2x8 joists under a 40 psf live load. Span tables in the IRC show that 2x8 joists at 24" o.c. typically have a maximum allowable span of approximately 10–11 feet for a 40 psf live load, depending on wood species and grade. At 12 feet, the span exceeds those limits. The combination of maximum spacing and excessive span creates a cumulative structural deficiency.

Why the Other Options Are Wrong

Option B: The joist depth is insufficient for the load

While joist depth affects span capacity, the depth (2x8 = 7.25 inches) is not itself insufficient as an isolated concern — the problem is the combination of wide spacing and long span. Framing the issue solely as 'depth is insufficient' misidentifies which variable is the root cause.

Option C: The spacing is too wide for the span length

While the 24" spacing is too wide for this span, selecting only the spacing as the concern is incomplete. The question asks for the primary concern, which encompasses both factors together — the span at 12 feet also independently exceeds code limits for this joist at this spacing.

Option D: The span is acceptable for the joist size

The 12-foot span is NOT acceptable for 2x8 joists at 24" o.c. under 40 psf loading. Span tables confirm that 12 feet exceeds the allowable span for this combination. This answer is factually incorrect.

Memory Technique

Remember: 'Two strikes, you're out.' When both spacing (24" o.c. is the widest common residential spacing) and span (12 feet) are at or beyond their individual maximums, the combination fails. Either factor alone might be borderline — together, they definitely exceed code.

Was this explanation helpful?

More Michigan Questions

A residential foundation wall in Michigan is 8 feet high with 2 feet above grade. The backfill exerts lateral pressure of 30 psf per foot of depth. What is the maximum lateral pressure at the bottom of the foundation wall?

A builder discovers that the electrical service entrance was installed without proper permits. According to Michigan law, what is the most appropriate next step?

What is the maximum allowable span for a 2x8 floor joist (Grade 2 Douglas Fir) at 16" O.C. with 40 psf live load and 10 psf dead load according to Michigan Building Code span tables?

According to Michigan Building Code, what is the maximum height of a wood-framed bearing wall using 2x4 studs with standard construction?

A homeowner requests to convert a bedroom into a bathroom on the second floor. What is the primary Michigan code concern the builder must address?

According to Michigan plumbing regulations, what is the minimum pipe size required for a water service line serving a single-family residence?

A contractor is building a basement foundation wall that is 8 feet high and will retain 6 feet of soil. What is the minimum wall thickness required by the Michigan Building Code for poured concrete?

A homeowner wants to install a gas fireplace in their living room. The contractor notices the existing gas line is 1/2 inch black iron pipe. For a 40,000 BTU fireplace with a 25-foot run, is this pipe size adequate according to Michigan gas code?

During a framing inspection, the building official notes that the contractor used 2x4 studs at 24 inches on center for an exterior wall. According to Michigan Building Code, what is the maximum wall height allowed for this configuration?

A contractor is installing a beam to support floor joists. The beam must carry a total load of 8,000 pounds over a 12-foot span. If the allowable fiber stress for the lumber grade is 1,200 psi, what is the minimum required section modulus?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.