A building inspector finds that stair risers vary between 7.5 inches and 8.25 inches in height. According to Michigan Building Code, is this acceptable?

Correct Answer

A) No, the variation exceeds 3/8 inch tolerance

Michigan Building Code requires riser heights to be uniform with a maximum variation of 3/8 inch. The 0.75 inch variation (8.25 - 7.5) exceeds this tolerance.

Answer Options
A
No, the variation exceeds 3/8 inch tolerance
B
Yes, the variation is within 3/8 inch tolerance
C
Yes, all risers are within the 4-8 inch range
D
No, all risers must be exactly the same height

Why This Is the Correct Answer

Michigan Building Code (aligned with IRC) requires that stair riser heights be uniform, with a maximum allowable variation of 3/8 inch (0.375 inches) between the tallest and shortest riser in a flight. Here, 8.25 − 7.5 = 0.75 inches of variation, which is double the 3/8-inch tolerance. This fails code and is not acceptable.

Why the Other Options Are Wrong

Option B: Yes, the variation is within 3/8 inch tolerance

Option B ('Yes, the variation is within 3/8 inch tolerance') is incorrect. The actual variation is 0.75 inches, which exceeds the 3/8-inch (0.375-inch) maximum. This answer would only be correct if the difference were 0.375 inches or less.

Option C: Yes, all risers are within the 4-8 inch range

Option C ('Yes, all risers are within the 4–8 inch range') is incorrect on two counts: first, 8.25 inches actually exceeds the maximum 8.25-inch riser height limit (right at the edge), but more importantly, code requires uniformity — individual risers being within range does not satisfy the requirement if the variation between risers exceeds 3/8 inch.

Option D: No, all risers must be exactly the same height

Option D ('No, all risers must be exactly the same height') is incorrect. Code does not demand perfect uniformity — it allows a 3/8-inch variance to account for real-world construction tolerances. The answer is 'no, it is not acceptable,' but the reason is that the variation exceeds 3/8 inch, not that absolute uniformity is required.

Memory Technique

Remember '3/8 inch = stair step consistency.' Picture a spirit level — if the difference between your highest and lowest riser tips the level more than 3/8 inch, you fail inspection.

Was this explanation helpful?

More Michigan Questions

A residential foundation wall in Michigan is 8 feet high with 2 feet above grade. The backfill exerts lateral pressure of 30 psf per foot of depth. What is the maximum lateral pressure at the bottom of the foundation wall?

A builder discovers that the electrical service entrance was installed without proper permits. According to Michigan law, what is the most appropriate next step?

What is the maximum allowable span for a 2x8 floor joist (Grade 2 Douglas Fir) at 16" O.C. with 40 psf live load and 10 psf dead load according to Michigan Building Code span tables?

According to Michigan Building Code, what is the maximum height of a wood-framed bearing wall using 2x4 studs with standard construction?

A homeowner requests to convert a bedroom into a bathroom on the second floor. What is the primary Michigan code concern the builder must address?

According to Michigan plumbing regulations, what is the minimum pipe size required for a water service line serving a single-family residence?

A contractor is building a basement foundation wall that is 8 feet high and will retain 6 feet of soil. What is the minimum wall thickness required by the Michigan Building Code for poured concrete?

A homeowner wants to install a gas fireplace in their living room. The contractor notices the existing gas line is 1/2 inch black iron pipe. For a 40,000 BTU fireplace with a 25-foot run, is this pipe size adequate according to Michigan gas code?

During a framing inspection, the building official notes that the contractor used 2x4 studs at 24 inches on center for an exterior wall. According to Michigan Building Code, what is the maximum wall height allowed for this configuration?

A contractor is installing a beam to support floor joists. The beam must carry a total load of 8,000 pounds over a 12-foot span. If the allowable fiber stress for the lumber grade is 1,200 psi, what is the minimum required section modulus?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.