EstatePass
MichiganBuilderhard50% of exam part

A builder is constructing a two-story house and needs to size the footing for a concentrated load from a support column. The column carries 25,000 pounds and the soil bearing capacity is 2,000 psf. What minimum footing area is required?

Correct Answer

A) 12.5 square feet

Required footing area = 25,000 lbs ÷ 2,000 psf = 12.5 square feet minimum.

Answer Options
A
12.5 square feet
B
17.5 square feet
C
10.5 square feet
D
15.0 square feet

Why This Is the Correct Answer

Option A is correct. The required footing area is calculated by dividing the column load by the allowable soil bearing capacity: Area = Load ÷ Soil Bearing Capacity = 25,000 lbs ÷ 2,000 psf = 12.5 square feet. This is the fundamental footing design equation.

Why the Other Options Are Wrong

Option B: 17.5 square feet

17.5 square feet is incorrect. This result cannot be derived from the given values using the correct formula. It may result from using an incorrect soil bearing value (e.g., 25,000 ÷ 1,428 ≈ 17.5) or from adding extraneous values. The calculation is straightforward: 25,000 ÷ 2,000 = 12.5.

Option C: 10.5 square feet

10.5 square feet is incorrect. This is less than the required 12.5 square feet. An undersized footing would cause the soil bearing pressure to exceed the allowable limit, leading to settlement or foundation failure. This may result from using a higher soil bearing value in the denominator (e.g., 25,000 ÷ 2,381 ≈ 10.5).

Option D: 15.0 square feet

15.0 square feet is incorrect. While 15 square feet would be a safe (conservative) footing, it is not the minimum required. The minimum is 12.5 square feet. A 15 sq ft footing might be selected in practice for ease of construction (e.g., a 4' × 4' = 16 sq ft pad), but the code-minimum calculation yields 12.5 sq ft.

Memory Technique

The footing formula is: Area = Load / Bearing Capacity. Think of it as 'spreading the load': the footing spreads the column load over enough soil area so that pressure on the soil doesn't exceed its capacity. Pressure = Force / Area, rearranged: Area = Force / Pressure. Units check: lbs ÷ lbs/ft² = ft².

Was this explanation helpful?

More Michigan Questions

A residential foundation wall in Michigan is 8 feet high with 2 feet above grade. The backfill exerts lateral pressure of 30 psf per foot of depth. What is the maximum lateral pressure at the bottom of the foundation wall?

A builder discovers that the electrical service entrance was installed without proper permits. According to Michigan law, what is the most appropriate next step?

What is the maximum allowable span for a 2x8 floor joist (Grade 2 Douglas Fir) at 16" O.C. with 40 psf live load and 10 psf dead load according to Michigan Building Code span tables?

According to Michigan Building Code, what is the maximum height of a wood-framed bearing wall using 2x4 studs with standard construction?

A homeowner requests to convert a bedroom into a bathroom on the second floor. What is the primary Michigan code concern the builder must address?

According to Michigan plumbing regulations, what is the minimum pipe size required for a water service line serving a single-family residence?

A contractor is building a basement foundation wall that is 8 feet high and will retain 6 feet of soil. What is the minimum wall thickness required by the Michigan Building Code for poured concrete?

A homeowner wants to install a gas fireplace in their living room. The contractor notices the existing gas line is 1/2 inch black iron pipe. For a 40,000 BTU fireplace with a 25-foot run, is this pipe size adequate according to Michigan gas code?

During a framing inspection, the building official notes that the contractor used 2x4 studs at 24 inches on center for an exterior wall. According to Michigan Building Code, what is the maximum wall height allowed for this configuration?

A contractor is installing a beam to support floor joists. The beam must carry a total load of 8,000 pounds over a 12-foot span. If the allowable fiber stress for the lumber grade is 1,200 psi, what is the minimum required section modulus?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.