epa-608-type-3Recovery & Evacuationmedium

A chiller is fitted with a factory pump-out unit and a storage tank, and the entire charge is now sitting in that tank. What still has to be done before the machine's waterbox covers come off?

Correct Answer

B) The chiller itself has to be pulled to the required level, because storing the charge on site changes nothing

Moving the charge from the shell into an onboard storage tank is a transfer, not the end of the job. Refrigerant vapor is still in the machine, more is still dissolved in the oil, and the required level is written for the appliance being opened. The pump-out unit gets the machine most of the way there quickly, but the last stretch is still made with recovery equipment and the reading is still taken at the shell before anyone breaks into it.

Answer Options
A
Nothing further is needed, because moving the charge into the plant's own tank satisfies the rule
B
The chiller itself has to be pulled to the required level, because storing the charge on site changes nothing
C
The storage tank has to be pulled to the required level, because the charge is now the tank's contents
D
The chiller has to be brought to zero gauge pressure, because the charge is no longer inside the shell

Why This Is the Correct Answer

The evacuation requirement attaches to the appliance that is about to be opened. A pump-out unit and storage tank move the bulk of the charge efficiently, but the shell has to reach twenty-five millimeters of mercury absolute before the refrigerant circuit is opened, because vapor and refrigerant coming out of the oil are still inside.

Why the Other Options Are Wrong

Option A: Nothing further is needed, because moving the charge into the plant's own tank satisfies the rule

Transferring the charge into an onboard tank is a useful head start, but it leaves vapor in the shell and refrigerant in the oil, so the required level has not been met.

Option C: The storage tank has to be pulled to the required level, because the charge is now the tank's contents

The storage tank is a container being filled, not the appliance being opened. Nothing requires a full tank to be pulled into a vacuum, and doing so would empty it.

Option D: The chiller has to be brought to zero gauge pressure, because the charge is no longer inside the shell

Zero gauge pressure is the very high-pressure appliance figure. A low-pressure machine at atmospheric pressure still holds a great deal of refrigerant vapor.

Memory Technique

The tank holds the charge; the shell holds the requirement.

Reference Hint

The required evacuation level applies to the appliance being opened, whatever container the charge has been moved into.

Was this explanation helpful?

More epa-608-type-3 Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.