epa-608-type-3Recovery & Evacuationmedium

An owner asks how many pounds of refrigerant the rules allow to be left inside a chiller once the recovery has been signed off. What is the correct answer to give him?

Correct Answer

D) The rule is written as a pressure level, so no residual weight is specified at all

The evacuation table sets a pressure that the appliance has to reach, not a quantity that may remain. How many pounds are left at that pressure depends on the size of the machine, how much oil it holds and how warm it is, and none of that is regulated. A technician documents the level reached and the amount recovered. Any answer expressed as a residual weight or a percentage of the charge is inventing a rule that does not exist.

Answer Options
A
The limit is one percent of the nameplate charge, measured by weighing the cylinders
B
The limit is ten pounds for any appliance holding more than two hundred pounds
C
The limit is whatever the recovery unit's own certification label states as residual
D
The rule is written as a pressure level, so no residual weight is specified at all

Why This Is the Correct Answer

Compliance is demonstrated by a pressure reading taken at the appliance, because pressure is what a technician can actually measure at the end of a recovery. The regulation never states a permitted residual quantity, and the amount left behind naturally varies with machine size and temperature. What goes on the record is the level reached and the quantity recovered.

Why the Other Options Are Wrong

Option A: The limit is one percent of the nameplate charge, measured by weighing the cylinders

Percentage-of-charge limits belong to leak rate provisions, not to evacuation. Nothing in the evacuation requirement is written as a share of the charge.

Option B: The limit is ten pounds for any appliance holding more than two hundred pounds

This borrows the two hundred pound split from the high-pressure rows of the evacuation table and attaches a weight to it that the table never contained.

Option C: The limit is whatever the recovery unit's own certification label states as residual

A recovery unit's certification says it can reach a required level. It says nothing about how much refrigerant may lawfully remain in an appliance.

Memory Technique

The rule measures pressure, not pounds. The scale is for the cylinder, the gauge is for the machine.

Reference Hint

Evacuation requirements are stated as pressure levels reached at the appliance, never as a permitted residual quantity of refrigerant.

Was this explanation helpful?

More epa-608-type-3 Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.