What should a technician do about the water in the chiller tubes before pulling a deep vacuum on the machine?

Correct Answer

A) Drain the tubes or keep the water circulating through them

As refrigerant is pulled out of a low-pressure machine the saturation temperature inside the shell falls, and standing water in the evaporator or condenser tubes can freeze solid. Ice expands, splits the tubes, and turns a routine recovery into a retubing job that costs far more than the refrigerant ever did. The fix is simple: either drain the water side completely before evacuating, or keep pumps running so the water is always moving and carrying heat into the bundle. Both approaches are accepted practice on Type III work.

Answer Options
A
Drain the tubes or keep the water circulating through them
B
Add a corrosion inhibitor to the chilled water loop
C
Fill the tubes completely and close both isolation valves
D
Lower the chilled water setpoint to forty degrees F

Why This Is the Correct Answer

Removing the water eliminates the freeze hazard entirely, and keeping it flowing supplies a steady heat load that holds the tube temperature above freezing while the vacuum deepens. Either step protects the bundle. Skipping both is the single most expensive mistake a technician can make on a low-pressure chiller recovery.

Why the Other Options Are Wrong

Option B: Add a corrosion inhibitor to the chilled water loop

Corrosion inhibitor protects metal from rust and scale over the long term. It does nothing to change the freezing point in any meaningful way and offers no protection during a deep evacuation.

Option C: Fill the tubes completely and close both isolation valves

Trapping a full bundle of standing water with the valves closed is the worst case. The water cannot move, it cannot pick up heat from anywhere, and it has nowhere to expand when it turns to ice.

Option D: Lower the chilled water setpoint to forty degrees F

The chilled water setpoint only matters while the machine is running and making cooling. Once recovery starts the controller is out of the picture and the setpoint has no effect on tube temperature.

Memory Technique

Drain it or drive it: the water either leaves the tubes or keeps moving through them.

Reference Hint

Freeze protection of the water side is standard Type III service practice during recovery under 40 CFR Part 82, Subpart F.

Was this explanation helpful?

More epa-608-type-3 Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.