On a low-pressure centrifugal chiller running at load, how do the evaporator and condenser sit relative to atmospheric pressure?

Correct Answer

D) The evaporator is under a vacuum while the condenser sits slightly above atmospheric

Pressure follows saturation temperature. The evaporator holds refrigerant near the chilled water temperature, well below the refrigerant's atmospheric boiling point, so it sits in a vacuum. The condenser holds refrigerant near the condensing water temperature, which is above that boiling point, so it carries a small positive pressure. That split is what makes the machine both leak air in at the low side and require a rupture disc rated only a little above atmospheric on the high side.

Answer Options
A
The whole machine sits in a deep vacuum from the evaporator through the condenser
B
Both vessels operate at several hundred psig, as in any other chiller
C
The evaporator is slightly above atmospheric while the condenser is under a vacuum
D
The evaporator is under a vacuum while the condenser sits slightly above atmospheric

Why This Is the Correct Answer

The evaporator runs cold enough that the refrigerant's saturation pressure falls below atmospheric, producing the vacuum that defines the class. The condenser runs warm enough that the saturation pressure rises slightly above atmospheric. Understanding this split explains both why air enters at the low side and why the relief device is set so low.

Why the Other Options Are Wrong

Option A: The whole machine sits in a deep vacuum from the evaporator through the condenser

The condenser must reject heat at a temperature above the cooling water, and at that temperature the low-pressure refrigerant carries a small positive pressure rather than a vacuum.

Option B: Both vessels operate at several hundred psig, as in any other chiller

Several hundred psig describes a high-pressure refrigerant. Low-pressure machines operate within a few psi of atmospheric across the whole circuit.

Option C: The evaporator is slightly above atmospheric while the condenser is under a vacuum

This reverses the machine. The cold vessel is the one in a vacuum, and the warm vessel is the one that goes slightly positive.

Memory Technique

Cold side sucks, warm side pushes, and neither one is far from the room.

Reference Hint

Low-pressure appliance evaporators run below atmospheric pressure; the condenser runs slightly above it because the condensing temperature exceeds the refrigerant's atmospheric boiling point.

Was this explanation helpful?

More epa-608-type-3 Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.