A low-pressure chiller's rupture disc has a discharge line running from it. Where does that line have to terminate?
Correct Answer
A) Outside the building, positioned away from openings and places where people are
If a relief device operates it will discharge a large part of the machine's charge in seconds. Sending that into the room would displace the air in it and endanger anyone inside, so the discharge line runs to the outdoors and terminates clear of doors, windows, air intakes and anywhere people gather. The line is kept full size and free of any valve or plug throughout, because anything that restricts it defeats the relief device it serves.
Why This Is the Correct Answer
The purpose of routing the relief discharge outdoors is to keep a sudden release of the entire charge away from the people in the machine room. The termination is placed clear of openings and occupied areas so that what comes out does not come straight back in, and the line stays unobstructed over its whole length.
Why the Other Options Are Wrong
Option B: In the machine room, at high level so the vapor disperses under the ceiling
Discharging inside the room puts the entire charge into the space people would be evacuating through, regardless of how high the outlet is.
Option C: Into the building's exhaust duct, so the vapor is diluted by the general exhaust
A general exhaust duct is not sized for a sudden release of an entire chiller charge, and it may serve other parts of the building.
Option D: Into a recovery cylinder mounted on the wall, so a relief event is captured
No cylinder could accept the flow from a relief event, and a closed vessel on the end of a relief line is itself a restriction.
Memory Technique
When the disc goes, the whole charge goes with it. Point it somewhere nobody is standing.
Reference Hint
Pressure relief discharge from a refrigeration machine is piped to the outdoors, away from building openings and occupied areas.
More epa-608-type-3 Questions
Some jobs on a chiller count as a major repair under the refrigerant rules, which changes what a technician is allowed to do with a badly leaking machine. Which job falls into that category?
An owner asks how many pounds of refrigerant the rules allow to be left inside a chiller once the recovery has been signed off. What is the correct answer to give him?
The motor of a hermetic centrifugal chiller sits inside the pressure boundary rather than outside it on a shaft. What follows from that construction?
An oxygen monitor is used to decide whether a chiller machine room is safe to enter after a refrigerant release. Below what oxygen reading is the atmosphere treated as oxygen deficient?
A refrigerant vapor detector in a chiller machine room reaches its alarm level. Besides sounding, what is that alarm expected to do?
Which piece of equipment requires a technician to hold Type III certification before it may be serviced?
What property of the refrigerant is what actually places an appliance into the low-pressure category?
During normal operation, what condition exists inside the evaporator of a running low-pressure centrifugal chiller?
In what unit is the required final recovery vacuum for a low-pressure appliance normally expressed?
What should a technician do about the water in the chiller tubes before pulling a deep vacuum on the machine?
People Also Study
Business & Financial Management
120 questions Β· 70% to pass
Contract Administration
60 questions Β· 70% to pass
Project Management
60 questions Β· 70% to pass
Related Study Resources
Previous Question
During recovery from a centrifugal chiller the technician needs to know when the liquid phase has finished and the slow vapor phase is starting. What tells him that?
Next Question
Chilled water is finding its way into the refrigerant side of a low-pressure chiller. Which failure allows that to happen?