A chiller has just been retubed and is being prepared to go back into service. What has to be done before the charge is returned to it?

Correct Answer

D) The water side is pressure tested and the shell is leak tested and then evacuated to dry it

A retube disturbs every tube-to-tube-sheet joint, so the water side is pressure tested to prove those joints hold before anyone puts refrigerant back into the shell. The refrigerant side is leak tested within the low pressure ceiling that applies to these machines, and then the shell is evacuated to pull out the air and moisture it took on during the weeks it stood open. Only after all three steps does the charge go back in.

Answer Options
A
The purge unit is run for a day so the shell is cleared of the air it took on while open
B
The charge is weighed in slowly, and the machine is leak tested at operating pressure afterward
C
The oil is changed after the first week of operation, once the new tubes have settled in
D
The water side is pressure tested and the shell is leak tested and then evacuated to dry it

Why This Is the Correct Answer

Three separate things have to be proven before a rebuilt machine is charged: that the new tube joints hold water, that the refrigerant side is tight, and that the shell is dry. Each has its own test, and skipping any one of them means either flooding the new bundle or charging a machine full of moist air, which starts acid formation on day one.

Why the Other Options Are Wrong

Option A: The purge unit is run for a day so the shell is cleared of the air it took on while open

A purge unit is not a substitute for evacuation. It removes gas slowly and cannot deal with the moisture the machine took on while it stood open.

Option B: The charge is weighed in slowly, and the machine is leak tested at operating pressure afterward

Leak testing after the charge is in leaves the technician with a machine full of refrigerant and a leak, which is the situation the tests exist to prevent.

Option C: The oil is changed after the first week of operation, once the new tubes have settled in

An oil change a week later does nothing about air and moisture that went in with the charge on the first day.

Memory Technique

Test the water, test the shell, dry the shell, then charge. Four steps, always in that order.

Reference Hint

A rebuilt appliance is leak tested and evacuated to remove air and moisture before the refrigerant charge is returned.

Was this explanation helpful?

More epa-608-type-3 Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.