A running low-pressure chiller has a leak at a joint on its condenser. What is happening at that joint while the machine is loaded?

Correct Answer

C) Refrigerant is escaping, because the condenser runs slightly above atmospheric pressure at load

A running low-pressure chiller is not under vacuum everywhere. The evaporator sits below atmospheric pressure, but the condenser is pushed slightly above it as the machine rejects heat. A leak on the condenser therefore loses refrigerant while the machine runs, and it draws air in once the machine shuts down and the pressure falls back. That is why a detector can find a condenser leak on a running machine while the evaporator end shows nothing at all.

Answer Options
A
Nothing moves either way, because the condenser sits exactly at atmospheric pressure at load
B
Air is drawn in, because every part of a low-pressure machine is under a vacuum at all times
C
Refrigerant is escaping, because the condenser runs slightly above atmospheric pressure at load
D
Water vapor is drawn in, because the condenser is the coldest surface on the machine at load

Why This Is the Correct Answer

The pressure profile across a running machine decides the direction of every leak on it. The condenser is above atmospheric at load, so a leak there pushes refrigerant out and can be found with an ordinary electronic detector. The same joint reverses direction on shutdown, which is why these machines both lose charge and accumulate air over a season.

Why the Other Options Are Wrong

Option A: Nothing moves either way, because the condenser sits exactly at atmospheric pressure at load

The condenser is above atmospheric at load rather than at it, which is exactly why a leak there behaves differently from one on the evaporator.

Option B: Air is drawn in, because every part of a low-pressure machine is under a vacuum at all times

The evaporator is under a vacuum; the condenser is not. Treating the whole machine as a vacuum vessel is the most common error on these questions.

Option D: Water vapor is drawn in, because the condenser is the coldest surface on the machine at load

The condenser is the hottest part of the machine at load, not the coldest, and nothing is drawing water vapor into it.

Memory Technique

Cold end sucks, hot end blows. The machine is a vacuum machine only at one end.

Reference Hint

On a running low-pressure chiller the evaporator is below atmospheric pressure and the condenser is slightly above it.

Was this explanation helpful?

More epa-608-type-3 Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.