A leak has been found on a large low-pressure chiller that falls under the leak repair provisions. Within what period does the rule expect that leak to be repaired?
Correct Answer
C) Within thirty days of the date the leak was found by the servicing technician
Once a leak has been identified on an appliance covered by the leak repair provisions, the clock starts on the day of discovery and the owner has thirty days to complete the repair. Extensions exist for specific situations, such as equipment that has to be shut down at a time of year the plant cannot manage, but the base period is thirty days. Nothing in the rule allows a leak to be logged and left until the next season.
Why This Is the Correct Answer
The repair period runs from the date the leak is discovered, and it is thirty days. That period is short on purpose, because refrigerant continues to escape and moisture continues to enter for as long as the leak is open. The owner is the party responsible for meeting it, and the dates of discovery and repair both go into the service record.
Why the Other Options Are Wrong
Option A: Within seven days of the date the leak was found by the servicing technician
A week would be unworkable for equipment that often has to be scheduled around a plant's load, and no such period appears in the rule.
Option B: Within ninety days of the date the leak was found by the servicing technician
Ninety days is far longer than the rule allows and would let a chiller lose a large share of its charge before anyone acted.
Option D: Within one year of the date the leak was found by the servicing technician
A year is roughly a full cooling season. Allowing that would defeat the purpose of having leak repair provisions at all.
Memory Technique
One month to fix it. Thirty days from the day you found it, not the day you got around to it.
Reference Hint
Leaks on appliances covered by the leak repair provisions must be repaired within thirty days of discovery.
More epa-608-type-3 Questions
Some jobs on a chiller count as a major repair under the refrigerant rules, which changes what a technician is allowed to do with a badly leaking machine. Which job falls into that category?
An owner asks how many pounds of refrigerant the rules allow to be left inside a chiller once the recovery has been signed off. What is the correct answer to give him?
The motor of a hermetic centrifugal chiller sits inside the pressure boundary rather than outside it on a shaft. What follows from that construction?
An oxygen monitor is used to decide whether a chiller machine room is safe to enter after a refrigerant release. Below what oxygen reading is the atmosphere treated as oxygen deficient?
A low-pressure chiller's rupture disc has a discharge line running from it. Where does that line have to terminate?
A refrigerant vapor detector in a chiller machine room reaches its alarm level. Besides sounding, what is that alarm expected to do?
Which piece of equipment requires a technician to hold Type III certification before it may be serviced?
What property of the refrigerant is what actually places an appliance into the low-pressure category?
During normal operation, what condition exists inside the evaporator of a running low-pressure centrifugal chiller?
In what unit is the required final recovery vacuum for a low-pressure appliance normally expressed?
People Also Study
Business & Financial Management
120 questions Β· 70% to pass
Contract Administration
60 questions Β· 70% to pass
Project Management
60 questions Β· 70% to pass
Related Study Resources
Previous Question
A machine room holds chillers charged with R-123, and the vapor monitor has to be set with the refrigerant's exposure limit in mind. What is the manufacturer's allowable exposure limit for R-123 as an eight hour average?
Next Question
Why must the relief piping downstream of a chiller's rupture disc never be plugged, valved shut or blocked?