An EV supply equipment nameplate input is 40 amperes and no permitted load-management reduction applies. What branch-circuit ampacity is required?
- A80 amperes
- B32 amperes
- 50 amperes
- D40 amperes
Why C is correct
EV charging is treated as continuous in this case. Multiplying the 40-ampere maximum load by 125 percent gives a required branch-circuit ampacity of 50 amperes.