A service calculation contains 84 amperes of noncontinuous load and 32 amperes of continuous load. Ignoring other demand factors, what calculated current results?
- 124 amperes
- B116 amperes
- C145 amperes
- D105.6 amperes
Why A is correct
Apply 125 percent only to the continuous portion: 32 amperes times 1.25 equals 40 amperes. Add the 84-ampere noncontinuous portion to obtain 124 amperes.