1. A storage water heater receives cold water through a pressure-reducing valve with an integral check. Under unamended 2021 IPC Section 607.3, what must be provided downstream of the check and pressure-reducing valve on the heater cold-water supply?
- AA hose bibb that an occupant opens when pressure rises
- BA relief valve with its pressure setting increased above the heater rating
- CAn additional check valve on the hot-water outlet
- A thermal expansion control device, sized as required for the installation
Where to look it up
https://www.ncosfm.gov/b-1-2024-ncpc/open
Why D is correct
Section 607.3 places thermal expansion control downstream of the check valves, pressure-reducing valves and backflow preventers on the cold supply. Expansion tanks are sized under manufacturer instructions to keep system pressure within the Section 604.8 limit. Section 504.4 prohibits using the relief valve to control thermal expansion. A dripping relief valve still requires diagnosis; it does not by itself establish one cause or one repair. See PDF pp.67 and 86. Source: 2021 IPC model base text reproduced in NC OSFM comparison document, https://www.ncosfm.gov/b-1-2024-ncpc/open