An arc fault device does not monitor current magnitude the way an overcurrent device does. It watches the electrical waveform for the signature of arcing — the erratic, high-frequency pattern produced when current jumps a gap rather than flowing through metal. A circuit with a loose terminal, a damaged conductor, a nicked wire behind a plate, or a failing cord can carry perfectly ordinary current and light a lamp normally while arcing intermittently at that fault. The device catching it is exactly what it is for, so a trip on a circuit that seems to be working is evidence of a fault the occupant cannot see, not evidence that the device is faulty. The inspector reports the trip, resists the temptation to conclude nuisance, and recommends evaluation by an electrician — noting that some trips do come from the device itself or from certain appliance loads, which is part of what the evaluation determines.