An open ground means the receptacle's grounding terminal has no continuous path back to the panel's grounding system. In a house wired with modern cable that includes an equipment grounding conductor, the path exists by design, so a reading of open ground indicates the connection was broken somewhere: a grounding pigtail not made up in the box, a wire that backed out of a terminal, a device replaced without reconnecting the ground, or a break upstream affecting several outlets. The consequence is that fault current has no low-impedance route home, so a fault to the metal case of an appliance may energise it instead of tripping the breaker. The inspector reports the condition and recommends evaluation; identifying which connection failed requires opening boxes, which is beyond a visual inspection.