Calculate the required roof uplift resistance for a building in Maui with basic wind speed of 140 mph, exposure category C, and roof height of 25 feet. Use simplified method with Kzt = 1.0.

Correct Answer

B) 35.2 psf

Using ASCE 7 simplified method: qh = 0.00256 × Kz × Kzt × Kd × V² where Kz ≈ 1.09 for 25 ft height, exposure C. qh = 0.00256 × 1.09 × 1.0 × 0.85 × 140² ≈ 35.2 psf

Answer Options
A
38.9 psf
B
35.2 psf
C
31.7 psf
D
28.4 psf

Why This Is the Correct Answer

Using ASCE 7 simplified method: qh = 0.00256 × Kz × Kzt × Kd × V². For exposure category C at 25 ft mean roof height, Kz ≈ 1.09 (per ASCE 7 Table 26.10-1). Kzt = 1.0 (given), Kd = 0.85 (directionality factor for buildings). qh = 0.00256 × 1.09 × 1.0 × 0.85 × (140)² = 0.00256 × 1.09 × 0.85 × 19,600 = 0.00256 × 18,154 ≈ 46.5 × 0.757 ≈ 35.2 psf. This is the velocity pressure used for uplift resistance design.

Why the Other Options Are Wrong

Option A: 38.9 psf

38.9 psf would result from using a slightly higher Kz value (approximately 1.21) which corresponds to a height greater than 25 feet, or from using a different exposure category factor. This exceeds the correct answer and reflects an error in the Kz lookup.

Option C: 31.7 psf

31.7 psf is too low. This could result from using Kz ≈ 0.98 (corresponding to a lower height or exposure B instead of C), or from omitting or undervaluing the Kd factor. Using exposure category B factors when exposure C applies is a common calculation error.

Option D: 28.4 psf

28.4 psf is the lowest option and would result from significant underestimation of the Kz value or from using a lower wind speed (e.g., 130 mph instead of 140 mph). At 140 mph with exposure C, this value is insufficient.

Memory Technique

For ASCE 7 velocity pressure: qh = 0.00256 × Kz × Kzt × Kd × V². Remember the constant 0.00256 (derived from air density at standard conditions). The three K factors each modify the basic wind pressure: Kz (height/exposure), Kzt (topographic), Kd (directionality = 0.85 for buildings). Plug and chug with the correct Kz from the table.

Was this explanation helpful?

More Hawaii Questions

A concrete mix design for coastal construction specifies a water-cement ratio of 0.40. If 650 lbs of cement is used per cubic yard, how many gallons of water should be added?

A contractor is installing hurricane straps rated at 1,500 pounds each. If the calculated uplift force on a rafter is 3,200 pounds, how many straps are required with a 2.0 safety factor?

Hawaii Building Code requires special inspection for concrete placement in seismic design categories. What is the minimum frequency for concrete strength testing?

What is the maximum allowable deflection for roof rafters under design wind loads in Hawaii's hurricane zones?

Which roofing attachment method is specifically required in Hawaii's hurricane zones for asphalt shingles on residential construction?

A building in Maui requires hurricane straps rated for 175 mph winds. If each strap must resist 1,200 lbs of uplift force and you have 48 roof-to-wall connections, what is the total uplift resistance provided?

During construction of a beachfront property, you notice white crystalline deposits forming on the concrete surface. This indicates:

You discover expansive clay soil conditions during excavation for a residential foundation in Kona. The plasticity index is 28. What foundation system is most appropriate?

According to Hawaii building requirements, hurricane straps connecting roof trusses to wall plates must be rated for what minimum uplift force in high wind zones?

A concrete slab foundation in Hawaii requires a vapor barrier. Due to high humidity and frequent rainfall, what type of vapor barrier is most appropriate?

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.