A chiller has been standing under a dry nitrogen holding charge and a technician now has to climb inside the shell. What has to be done to the space first?
Correct Answer
A) It has to be ventilated with fresh air and the oxygen content verified before entry
Nitrogen is harmless to breathe in air and lethal in place of it. A vessel that has held a nitrogen charge contains no oxygen at all, and a person leaning into it can lose consciousness in seconds with no warning sensation. Bleeding the pressure off does not fill the space with air. The shell is force ventilated, the atmosphere is tested for oxygen, and the entry proceeds under confined space rules with an attendant outside.
Why This Is the Correct Answer
The hazard is displacement rather than toxicity, and nitrogen gives no warning at all because it does not smell, irritate or trigger the body's response to suffocation. Only forced ventilation puts air back into the shell, and only a meter proves it worked. Testing before entry and continuing to monitor during it is the practice that makes the entry survivable.
Why the Other Options Are Wrong
Option B: It has to be brought to atmospheric pressure and left open for the shift before entry
Opening a vessel does not ventilate it. Heavy gas layers sit undisturbed inside a shell for a long time with no air movement to displace them.
Option C: It has to be warmed with the water pumps so that the nitrogen rises out of the shell
Warm water in the tubes does nothing to exchange the atmosphere inside the shell, and nitrogen does not conveniently rise out of an opening.
Option D: It has to be swept with dry refrigerant vapor so that the nitrogen is displaced downward
Sweeping with refrigerant vapor replaces one asphyxiant with another and wastes refrigerant doing it.
Memory Technique
Nitrogen is not poison, it is absence. You do not smell it because there is nothing there to smell.
Reference Hint
A vessel that has held nitrogen contains no oxygen; it must be ventilated and its atmosphere tested before entry.
More epa-608-type-3 Questions
Some jobs on a chiller count as a major repair under the refrigerant rules, which changes what a technician is allowed to do with a badly leaking machine. Which job falls into that category?
An owner asks how many pounds of refrigerant the rules allow to be left inside a chiller once the recovery has been signed off. What is the correct answer to give him?
The motor of a hermetic centrifugal chiller sits inside the pressure boundary rather than outside it on a shaft. What follows from that construction?
An oxygen monitor is used to decide whether a chiller machine room is safe to enter after a refrigerant release. Below what oxygen reading is the atmosphere treated as oxygen deficient?
A low-pressure chiller's rupture disc has a discharge line running from it. Where does that line have to terminate?
A refrigerant vapor detector in a chiller machine room reaches its alarm level. Besides sounding, what is that alarm expected to do?
Which piece of equipment requires a technician to hold Type III certification before it may be serviced?
What property of the refrigerant is what actually places an appliance into the low-pressure category?
During normal operation, what condition exists inside the evaporator of a running low-pressure centrifugal chiller?
In what unit is the required final recovery vacuum for a low-pressure appliance normally expressed?
People Also Study
Business & Financial Management
120 questions Β· 70% to pass
Contract Administration
60 questions Β· 70% to pass
Project Management
60 questions Β· 70% to pass
Related Study Resources
Previous Question
Where does a technician look up the exposure limit and first aid information for the refrigerant in a particular machine?
Next Question
After a low-pressure machine has reached the required level and the charge is out in cylinders, the technician wants to pull it deeper still to dry it out. Is a plain vacuum pump allowed for that?