As the recovery unit begins pulling the charge out of a chiller, what should the technician do with the machine's purge unit?

Correct Answer

D) Shut it off, so it does not discharge refrigerant vapor while the shell pressure is falling

Running the purge before recovery starts is good practice, because it takes non-condensable gas out while the machine is still at normal pressures and the purge can separate refrigerant properly. Once recovery begins the picture changes: the pressure in the condenser drops, the purge can no longer tell refrigerant from air, and everything it discharges goes outdoors. Shutting it off at the start of the recovery keeps that refrigerant in the machine where the recovery unit will capture it.

Answer Options
A
Set it to continuous, so the shell reaches the required level faster than recovery alone
B
Leave it running, so it keeps stripping non-condensable gas out of the shell as it empties
C
Switch its exhaust into the recovery hose, so whatever it removes goes into the cylinder
D
Shut it off, so it does not discharge refrigerant vapor while the shell pressure is falling

Why This Is the Correct Answer

A purge separates refrigerant from air by condensing the refrigerant, and that separation depends on the condenser being at its normal pressure. During recovery the pressure collapses, the separation fails and the purge simply pushes refrigerant vapor out of its exhaust. Turning it off at the start of the recovery is what keeps the charge in the machine and out of the atmosphere.

Why the Other Options Are Wrong

Option A: Set it to continuous, so the shell reaches the required level faster than recovery alone

A purge cannot pull a machine down. Setting it to run continuously only increases how much refrigerant leaves through its exhaust.

Option B: Leave it running, so it keeps stripping non-condensable gas out of the shell as it empties

The purge separates properly only at normal operating pressure. Once recovery starts, what it removes is refrigerant rather than air.

Option C: Switch its exhaust into the recovery hose, so whatever it removes goes into the cylinder

Purge exhaust piping is small and routed outdoors, and rerouting it into the recovery hose is neither practical nor a recognized procedure.

Memory Technique

Purge first, then pull. A purge running on a collapsing machine is just a chimney.

Reference Hint

The purge unit is run before recovery begins and shut off during recovery, because it cannot separate refrigerant from air at reduced pressure.

Was this explanation helpful?

More epa-608-type-3 Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.