During the final pull down on a low-pressure chiller the technician's absolute pressure gauge is holding steady at forty millimeters of mercury. What does that reading mean for the job?

Correct Answer

C) The machine is not there yet, and recovery has to continue until the reading falls further

Absolute pressure is measured up from a perfect vacuum, so a smaller number means a deeper vacuum. The requirement is twenty-five millimeters of mercury absolute, and forty is above it. The machine still holds more refrigerant than the rule allows and the recovery has to keep going. A reading that stalls at forty usually means air is being drawn in through a fitting, or that refrigerant is still boiling out of the oil charge.

Answer Options
A
The machine has gone too deep, and the vacuum has to be broken back before opening
B
The machine is at the requirement, because forty millimeters is the figure for a chiller
C
The machine is not there yet, and recovery has to continue until the reading falls further
D
The machine is past the requirement, since forty is a larger number than the figure required

Why This Is the Correct Answer

With absolute units the scale runs downward toward a perfect vacuum, so the requirement is a ceiling rather than a floor. Forty millimeters of mercury is higher than twenty-five, so the appliance has not reached the level and may not be opened. The technician keeps pulling and starts looking for what is holding the pressure up.

Why the Other Options Are Wrong

Option A: The machine has gone too deep, and the vacuum has to be broken back before opening

There is no such thing as too deep for the purposes of the rule. Going below the required figure is allowed and is often necessary before the machine will hold.

Option B: The machine is at the requirement, because forty millimeters is the figure for a chiller

Twenty-five millimeters is the chiller figure. Forty is a number a stalled recovery lands on, not a level anyone is permitted to stop at.

Option D: The machine is past the requirement, since forty is a larger number than the figure required

This reads the scale backward. In absolute units a larger number is a shallower vacuum, so forty millimeters is further from the target than twenty-five, not past it.

Memory Technique

Absolute pressure is a countdown, not a count-up. Zero would be a perfect vacuum.

Reference Hint

Absolute pressure counts up from a perfect vacuum, so the low-pressure requirement of twenty-five millimeters is reached by driving the reading down.

Was this explanation helpful?

More epa-608-type-3 Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.