The purge unit on an R-123 chiller has failed and its compressor has to be replaced. What has to happen to the refrigerant sitting inside that purge unit before it is opened up?

Correct Answer

C) It has to be recovered, because the purge unit is part of the appliance's refrigerant circuit

The purge unit is piped into the chiller's condenser and holds refrigerant in its own drum, condenser and lines. Opening it opens the refrigerant circuit of a low-pressure appliance, so whatever refrigerant it holds has to be recovered first. Nothing about its small size or its exhaust function creates an exemption. The small appliance limit describes factory-sealed units charged with five pounds or less, not a component bolted onto a chiller holding hundreds of pounds.

Answer Options
A
It can be vented off, because the purge unit's normal job is to discharge gas to the atmosphere
B
It can be left in place, because a purge holds less than the five pound small appliance limit
C
It has to be recovered, because the purge unit is part of the appliance's refrigerant circuit
D
It has to be logged and then released, because a purge drum's contents count as de minimis

Why This Is the Correct Answer

A purge unit is plumbed into the chiller and forms part of the same refrigerant circuit, so refrigerant inside it belongs to the appliance. Before the purge compressor is unbolted, that refrigerant is recovered with certified equipment the same way the main charge would be. The venting prohibition does not stop at the chiller shell.

Why the Other Options Are Wrong

Option A: It can be vented off, because the purge unit's normal job is to discharge gas to the atmosphere

The purge discharges non-condensable gas, not refrigerant. Treating the exhaust function as permission to release the refrigerant inside the unit is a deliberate venting violation.

Option B: It can be left in place, because a purge holds less than the five pound small appliance limit

The five pound figure describes factory-sealed small appliances. A purge bolted to a five hundred ton chiller is a component of a low-pressure appliance no matter how little it holds.

Option D: It has to be logged and then released, because a purge drum's contents count as de minimis

De minimis covers the traces that escape during a good-faith recovery, not a decision to empty a component into the room and write it down afterward.

Memory Technique

If refrigerant can get into it, the rules can get into it. The purge is part of the machine.

Reference Hint

Recovery is required before opening any part of the refrigerant circuit, including accessories such as the purge unit.

Was this explanation helpful?

More epa-608-type-3 Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.