After a low-pressure machine is closed back up following an open repair, what has to happen before the charge goes in?

Correct Answer

B) Evacuate the machine to pull out the air and moisture it took on while open

A machine that has been open to the room is full of air and water vapor. Both have to come out before the refrigerant goes in, and evacuation is what removes them. Relying on the purge unit instead is a common shortcut and a poor one: the purge is sized to handle the small amount of air that leaks in during normal operation, not a shell full of it, and every purge cycle carries refrigerant out with the air. Evacuating first protects the charge, the oil and the machine's efficiency.

Answer Options
A
Charge the machine and let the purge unit remove whatever air is left
B
Evacuate the machine to pull out the air and moisture it took on while open
C
Fill the machine with nitrogen and leave it under pressure until startup
D
Run the chilled water pumps for an hour so the tubes dry out

Why This Is the Correct Answer

Evacuation lowers the pressure enough to boil off moisture and to pull the air out of the vessel before any refrigerant is added. That leaves the machine clean and dry so the charge is not immediately contaminated with non-condensables and the purge unit is not asked to do work it was never sized for.

Why the Other Options Are Wrong

Option A: Charge the machine and let the purge unit remove whatever air is left

The purge unit handles the small ongoing air load of normal operation. Making it clear a shell full of air wastes refrigerant and takes a very long time.

Option C: Fill the machine with nitrogen and leave it under pressure until startup

Nitrogen under pressure is fine for storage or leak testing, but it must be removed by evacuation before charging, so this skips the necessary step.

Option D: Run the chilled water pumps for an hour so the tubes dry out

Running water pumps warms the tubes but does nothing about the air and moisture inside the refrigerant side of the machine.

Memory Technique

Evacuate for the load, purge for the leak. Purge units sip, they do not gulp.

Reference Hint

A machine opened for repair must be evacuated to remove air and moisture before charging; the purge unit is only for normal operating air ingress.

Was this explanation helpful?

More epa-608-type-3 Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.