A single evaporator tube has been identified as the source of a leak on an older chiller. What does plugging that tube accomplish?

Correct Answer

A) It seals the leak path temporarily, within the number of tubes the manufacturer allows to be plugged

Tapered plugs driven into both ends of the failed tube stop water crossing into the refrigerant side and get the machine through the season. It is a temporary measure. Each plugged tube takes surface out of service and the manufacturer sets a limit on how many may be plugged before the bundle has to be replaced. The machine still has to be dried out, and the leak still has to be recorded and dealt with under the same rules as any other repair.

Answer Options
A
It seals the leak path temporarily, within the number of tubes the manufacturer allows to be plugged
B
It restores the bundle to its original condition, so the machine may be returned to full rated duty
C
It cancels the repair obligation, because a plugged tube is no longer part of the water circuit
D
It replaces the need to dry the machine out, because the water path has been closed off at both ends

Why This Is the Correct Answer

Plugging closes the leak path through one tube and lets the machine run, at the cost of a little capacity. It is recognized as a temporary repair, and the manufacturer's plugging limit is what tells an owner when the bundle is finished. Everything else the failure caused, particularly the moisture in the machine, still has to be dealt with.

Why the Other Options Are Wrong

Option B: It restores the bundle to its original condition, so the machine may be returned to full rated duty

A plugged tube is a tube out of service. Capacity falls slightly with each one, and the bundle is not back to its original condition.

Option C: It cancels the repair obligation, because a plugged tube is no longer part of the water circuit

Nothing about plugging removes the repair and record keeping obligations that follow a leak on a covered appliance.

Option D: It replaces the need to dry the machine out, because the water path has been closed off at both ends

Water has already been inside the shell. Closing the path it came through does not remove the moisture it left behind.

Memory Technique

A plug buys a season, not a bundle.

Reference Hint

Plugging a failed tube is a temporary repair limited by the manufacturer's maximum number of plugged tubes.

Was this explanation helpful?

More epa-608-type-3 Questions

People Also Study

Related Study Resources

Practice More Contractor Exam Questions

Access all practice questions with progress tracking and adaptive difficulty to pass your contractor license exam.

Start Practicing

Disclaimer: EstatePass is an independent exam preparation platform and is not affiliated with, endorsed by, or connected to any state contractor licensing board, the Construction Industry Licensing Board (CILB), the Department of Business and Professional Regulation (DBPR), NASCLA, Pearson VUE, PSI, or any government agency. Exam requirements, fees, and regulations change frequently. Always verify current requirements with your state's licensing board before making decisions. Information shown was last verified on the dates indicated and may not reflect the most recent changes.